Hi guys,
Could do with some advice on a job I've got on this week.
A lady from holland who has a flat in a block of flats in London has had her gas supply totally removed from her flat, as she is dead against it. Now the problem is she only has a 60a fuse at the rifle board supplying her flat. A guy from EON came today to supposedly upgrade the main fuse to 100a and tails etc. But due to some miscommunication he thought he was only coming to remove the 60a fuse to kill power to the flat. Now when he came he said it wouldn't be easy to upgrade the rifle board fuse, as the service head only had 3x100a. And that to upgrade these would mean cutting off power to the whole block, and upgrading the mains from the road.
This is the new load
1 x 3kw? water heater
2 x 2kw heaters
1 x 1.5kw heater
1 x 1kw heater
1 x 1.9kw steamer
1 x 3.6kw cooker
1 x 3.2kw hob
1 x 2.2kw dishwasher
+ washing machine, dryer, towel rail
Now all this at full load would definitely use over 60a. Anyway the lady was advised by someone to order a wylex fuseboard with an inbuilt Wylex MESB-63NO 63a Contactor. She also had a dutch kitchen fitter bring over all the new items from holland.
I've never fitted one of these contactor's before and was wandering what would be the best way to arrange the circuits and how to wire in this contractor??? And would it be possible without upgrading the main fuse??
Cheers
Could do with some advice on a job I've got on this week.
A lady from holland who has a flat in a block of flats in London has had her gas supply totally removed from her flat, as she is dead against it. Now the problem is she only has a 60a fuse at the rifle board supplying her flat. A guy from EON came today to supposedly upgrade the main fuse to 100a and tails etc. But due to some miscommunication he thought he was only coming to remove the 60a fuse to kill power to the flat. Now when he came he said it wouldn't be easy to upgrade the rifle board fuse, as the service head only had 3x100a. And that to upgrade these would mean cutting off power to the whole block, and upgrading the mains from the road.
This is the new load
1 x 3kw? water heater
2 x 2kw heaters
1 x 1.5kw heater
1 x 1kw heater
1 x 1.9kw steamer
1 x 3.6kw cooker
1 x 3.2kw hob
1 x 2.2kw dishwasher
+ washing machine, dryer, towel rail
Now all this at full load would definitely use over 60a. Anyway the lady was advised by someone to order a wylex fuseboard with an inbuilt Wylex MESB-63NO 63a Contactor. She also had a dutch kitchen fitter bring over all the new items from holland.
I've never fitted one of these contactor's before and was wandering what would be the best way to arrange the circuits and how to wire in this contractor??? And would it be possible without upgrading the main fuse??
Cheers