Hello,

I bought a used generator and transfer switch from a Generac installer. He had a customer that was upgrading, so he bought their old one, and then I got his old one. Anyway, it is a 7kW unit with an automatic transfer switch + panel.

The generator is installed, starts up and runs, and I am now working on the wiring. Everything is hooked up on the generator side, but I am having trouble on the transfer switch side.

I understand where to wire the power, grounds and control wires, however, I am unsure where the neutrals go.

The instructions state to move the circuit with the neutral over to the new subpanel. That neutral would go to the neutral bus in the transfer switch/panel and the circuit in the transfer switch panel. The ground for the circuit remains in the main box.

The thing I don't understand is that there is only one lug to hook up a neutral wire. Wouldn't the neutral bus in the transfer switch need to be able to switch between neutrals depending on which source the power is coming from?
 

Attachments

  • IMG_20201103_134048.jpg
    IMG_20201103_134048.jpg
    159.3 KB · Views: 238
  • IMG_20201103_134057.jpg
    IMG_20201103_134057.jpg
    141.7 KB · Views: 60
Normally in the UK the neutral is switched over as the source (utility or generator) is often the point of commonality between the neutral (return for current under normal circumstances) and the earth (ground, return for current under fault conditions). The UK regulations do not allow that link N-E to take place inside the installation, or allow there being two links (to avoid spurious circulating currents in the earth structure).

However, the USA and some other places have different rules and so it is possible that the utility neutral is just left connected as all times, even when on generator. Again, in the UK that is a big no-no in case there is a fault and some worker on the utility side is exposed to a "live" neutral due to back-feed from the generator.

Hopefully one of our American members such as @Megawatt can reply as they will knowe far more than I do about this situation.
 
Yes, that was my thought as to why they need to be switched.

So, looking at the pictures, am I missing something as to where the neutrals would hook up to be switched?

I found the picture below on another forum, and it looks like they hooked the generator neutral to the neutral bar main lug, and the one going back to the main panel in a normal spot on the neutral bar.

This would be incorrect, no?
image.jpg
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Michigan
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Generac Automatic Transfer Switch Install
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
chriskay301,
Last reply from
chriskay301,
Replies
3
Views
2,153

Advert

Back
Top