Not so much an electrical question, but physically.

Got a customer out in the sticks who’s suffered with powercuts frequently during the recent storms.
Now, easy enough to fit a changeover switch, but in this case, the mains comes in in the centre of the house. Not a handy place to drill a hole to outside.

So, would you wire in a 32A (or 16, depending what genny they get) plug to the changeover, leave a long enough extension lead to reach a window, crossing their kitchen floor….

Don’t suggest a “widowmaker”
 
Had a look this morning, and the customer isnt adverse to spending a few bob.

He's going to be ordering a genny at £1500 anyway... One like the pic on Buzz's post above.
6kW, with 32A hookup on the 230v side.

They work from home, so there would be computers and broadband hub over the general lighting, fridge freezer and possibly electric hob... which i said, use only one, and not at the same time as kettle.

I was thinking a 4mm T&E run behind the kitchen kickboard to an outside wall, drill through and a BS4343 32A plug on the wall.
He would want the generator, however to be sighted away from here, as neighbours bedroom window is only 2m away... So a trailing extension lead from here to the genny, roughly 10m away
Also, the plug would be close to his outside oil boiler... there is a 10mm bonding conductor from the copper pipe back to the MET from here.
Bond between plug and pipe?

As the changeover switch needs to carry the load of the property in normal use, need to go with 100A, as i dont know the main fuse size...

So this?

With an enclosure containing a 32A MCB on the generator source... (although will the generator have that built in?)

There's already Henley blocks and a service isolator in the mains supply... and no problems with space.

And i'll mark up the existing CU to say which circuits are more vital than others.
 
They used to do a 100a twin or 4 pole main switch change over assembly that was two main switches linked together, one was upside down to the other so when one was on the other was off as a change over switch. I haven't seen one for ages and not sure how safe this set up is?! A 3 position switch is a much better option!
 
They used to do a 100a twin or 4 pole main switch change over assembly that was two main switches linked together, one was upside down to the other so when one was on the other was off as a change over switch. I haven't seen one for ages and not sure how safe this set up is?! A 3 position switch is a much better option!
TLC Electrical do a 125A c/o switch for £82.80 plus vat.It comprises a 4 pole 125A switch with suitable links.
Comes in a metal din enclosure.
Regards,
S
 
Thanks @sinewove hadn't seen them on there! I found one here

The only thing I don't like about them is there is no proper off position. On the rotary ones I have fitted they have on mains off Center and on generator, I prefer this as there is a definite off between the change over.

Ps just remembered that I fitted the TLC 63a rotary one some time ago on a farm and it was good quality and nice to fit too!
This one

Should imagine the 32a one is of a similar standard!
Sy
 
I was thinking a 4mm T&E run behind the kitchen kickboard to an outside wall, drill through and a BS4343 32A plug on the wall.
He would want the generator, however to be sighted away from here, as neighbours bedroom window is only 2m away... So a trailing extension lead from here to the genny, roughly 10m away
Can you put the inlet socket closer to the desired final location?

Also I would suggest making up a suitable H07RN-F lead, or get them to buy one you have checked is OK for the job.

Also, the plug would be close to his outside oil boiler... there is a 10mm bonding conductor from the copper pipe back to the MET from here.
Bond between plug and pipe?
Maybe, but the real issue is you need an earth rod as:
  • You cannot depend on the supply earth being present during power outage (a whole cable section could have been sliced)
  • You cannot rely on service pipes to do that job
As it might well be TN-C-S normally you then need 10mm bonding to the rod so taking a properly installed earth to the generator is not OK as 4mm T&E CPC far too small, so really I would add an earth rod to the gas pipe bond cable (and of course verify it is sound, etc).

As the changeover switch needs to carry the load of the property in normal use, need to go with 100A, as i dont know the main fuse size...

So this?
Looks fine, or the other 100A+ models others have just pointed to.
With an enclosure containing a 32A MCB on the generator source... (although will the generator have that built in?)
You probably don't needs that as the generator should have overload protection and so long as no Muppet puts a bigger generator above 32A on a 32A female plug to power it then no issue.

I would double check the generator has an output MCB and RCD, though I expect by that size they would be properly equipped and a TN-S source.
There's already Henley blocks and a service isolator in the mains supply... and no problems with space.

And i'll mark up the existing CU to say which circuits are more vital than others.
Excellent!
 
The generator RCD can give rise to further problems if the existing installation is protected by multiple RCDs/RCBOs. Existing earth leakage might be well below that required to trip any of the existing ones, but the sum of them might trip the generator RCD.
I know from experience that customers are not amused when this happens when they are struggling with rough weather and a power cut.
 
The generator RCD can give rise to further problems if the existing installation is protected by multiple RCDs/RCBOs. Existing earth leakage might be well below that required to trip any of the existing ones, but the sum of them might trip the generator RCD.
I know from experience that customers are not amused when this happens when they are struggling with rough weather and a power cut.
Very true, and this is sounding like a big enough generator that it might be a problem, but often if you have to shut off 2/3 of the circuits due to tight load limits you might get away with it.

Certainly worth checking out the accumulated leakage before it is cold, dark, wet, and no mains!
 
From experience, that type of small generator may also have a floating earth (I-S) and it's RCD configured such that it's the actual chassis/electrode being monitored through a CT and not the outgoing L/N inbalance - ergo if you have a fault to electrode downstream then it won't get seen.
 
From experience, that type of small generator may also have a floating earth (I-S) and it's RCD configured such that it's the actual chassis/electrode being monitored through a CT and not the outgoing L/N inbalance - ergo if you have a fault to electrode downstream then it won't get seen.
Seems an odd thing to do when it is big enough to power multiple circuits, etc, but I guess they have their reasons.

Certainly worth checking the manual / asking manufacturer, or at the very least doing a bond check N-E at the generator outlet.
 
Seems an odd thing to do when it is big enough to power multiple circuits, etc, but I guess they have their reasons.

Certainly worth checking the manual / asking manufacturer, or at the very least doing a bond check N-E at the generator outlet.
The two things I mostly have to ‘correct’ on hired-in gensets in muddy fields are making a PEN link and reworking where the RCD fits in the system
 

Reply to Generator back up for house in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
A couple of carbon monoxide detectors would be a good investment
Replies
12
Views
2K
  • Question
which has a better waveform,1000w or 2000w inverter, just confused
Replies
14
Views
4K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks