so e54 in your experience are you saying the generator dosnt need to be on its own earth mat (earth) and could you explain to me why we take an earth from the met to the lightining conductor cos in my mind were bringing a fault back into the building why dont we let the lightining strike just travel down rods and disperse in the general mass of the ground*** why give it a path back into the building
As stated previously, you need to provide an earth rod/mat connection to the generators N-E point/position, which will effectively earth the generators frame as well. And '''NOT'' a 200 ohm affair either!! lol!!
***If only lightning strikes always followed those made paths, and ONLY those paths to ground.. lol!! In reality lightning strikes don't always follow those made paths and can find/seek out other paths, by means of jumping or penetrating...
As for lightning protection, one reason is that the LP system will introduce an extraneous earth situation, say on the roof of a building where different services are present (A/C, Water Tanks, Aerial Installations etc. So to bring the LP to the same potential as the main supply earth, a link or bond is made, normally to the LP down conductor closest to the buildings main intake.
Another reason is that most buildings that support an LT system will be of reinforced concrete construction, (some systems will even use the reinforcement as part of LP the down conductor). It is more than likely that any decent strike on such a building, will reach any reinforcement (normally only around 25mm inside the concrete) anyway.
As this reinforcement will at some point or points be connected to the buildings power supply earthing arrangement, whether it be by a purposely made connection or otherwise it is again sensible to link the LP to the building earthing system. Last but certainly not least, it will effectively stop any jumping of lightning strikes from the LP system to any building earthed metalwork etc!!
The use of SPD's on electrical installations where LP systems are in place, will effectively reduce or even completely remove any lightning strike damage to the system... To be honest, i've never seen any damage caused by lightning strikes to LP protected buildings, that have been totally devoid of such devices, but i would now never not use them, as building system sophistication is increasing exponentially!! lol!!