Generator earth | on ElectriciansForums

Discuss Generator earth in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 7, 2012
Messages
66
Reaction score
9
Location
Scotland
Hi all, first post for some time! Currently installing power and lighting into a small cabin. Supply will be from a permanently connected generator and using a rod for earthing purposes. Carrying out testing today and only getting 197v between live and rod. Guessing I may need another rod which I didn't have with me but there was a couple of old steel beams concreted into the ground so I connected to them to see if it would help but no diffence. Is installing a few more rods going to help, if not I don't know what else to do!
 
Sounds like gen has an isolating transformer type output and might be intended to power a double insulated power tool? Gen details? (I can try to look it up on line)
 
Yes sounds like generator output is floating so you have an IT system not TN. You will need to investigate the N-E link options if you want TN.
 
There is no definitive answer. There are pros and cons for separated systems, although the larger the installation and the greater likelihood of undetected first earth faults the greater the argument in favour of earthed TN-S. BS7430 might have some useful info, see also points 11 & 12 here: OC 482/2: Electrical safety of independent low-voltage ac - http://www.hse.gov.uk/foi/internalops/ocs/400-499/oc482_2.htm

As to where to make an N-E link, maybe in the genny terminal box, maybe at the CU, the genny maker might have made specific provisions.

Don't forget that when you are testing the rod, it's not like an earth rod on TT where you're picking up an earth from the supplier's substation via the ground. Here you are the supplier and you are referencing your system to it.
 

Reply to Generator earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top