Hi Robbie,

If i am reading the regs right the 1667ohm would be for the rcd part to operate correctly but anything over the 0.72 would fail for over current protection?

You are mixing two different fault current paths up here, the 1667 ohms is max Zs , which is for the RCD part (if it is a 30mA device), which is an Earth fault path, which the RCD part takes care of for you.

The overcurrent/Short circuit fault path will be Phase to Phase, or Phase to Neutral, which as long as the OCPD rating (the 25A part) does not exceed the PSCC output capability of the generator, or at the circuit itself , will be fine.
 
Last edited:
Just and addition to above,^^^
You will need to measure your R1 + Rn, to see if this is less than your stated 0.72 ohms, also you may find that you only need a 1 or 5 second disconnection time as opposed to a 0.2 or 0.4, depending on the circuit arrangement and type of earthing system, this may then allow a higher permissable max reading with regard to overcurrent/Short circuit protection.
 
Last edited:
So could someone tell me if max zs for 25amp RCBO is 0.72ohms and test results are 3.4 ohms is this a pass or fail? I would take this as a fail all day long!
 
So could someone tell me if max zs for 25amp RCBO is 0.72ohms and test results are 3.4 ohms

As already said, anything below 1667 ohms for a 30mA RCD/RCBO is a pass for Zs (Earth fault Impedance)
 
I looked through the previous posts and cannot see any mention of 0.72, where did you get this figure from ?
 
Again you are mixing max Zs up with Over current protection.

Your Earth fault current is taken care of by the RCD part, which allows up to 1667 ohms for a 30mA device

Zs = Ze + (R1 + R2)
 
Last edited:
So what is the point on having that table then?? I am not used to testing where zs is higher than this table without it being a fail?
 
The OCP part follows a different path, being either R1 + Rn or R1 + R1, either phase to neutral, or phase to Phase, Ze does not play a part in this. You will probably find the fault path impedance is a lot lower (with no Ze to add).

Your EFLI path is taken care of by the RCD part.

The tables also relate to where an RCD is not used, as is the case in many applications.
 
Last edited:
As I said and the start of this posts,I am unfamiliar with these type of readings so wanted some experienced people to inform me,so these readings are acceptable that I am getting??
 
I will try to explain a bit.

Zs = Ze + (R1 +R2)

For instance a lighting circuit protected by a B type 6A MCB

If we had a Ze of say a 100 ohms, and an (R1 + R2) reading of 1 ohm.

A type B6 amp MCB requires 5 X 6A to break instantanously (5 being the multiplier for a B type device).

230/(5X6) = 230/30 = 7.6 ohms (max Zs)

Zs = Ze + (R1 + R2) = 100 + 1 = 101 ohms for our Zs value, clearly this value is far too high to trip the B6 MCB, so by adding a 30mA RCD, this will increase the max Zs allowed up to 1667 ohms, our circuit above will then trip to give the required disconnection time.
 
Last edited:
Using the above values for Short circuit/over current protection, assuming the same size CPC as our line conductor.

Our fault path this time being R1 + Rn, (R1 + Rn) = 1 ohm (which is a far lower reading without the much higher Ze), which is lower than the 7.6 ohms allowed, and so the MCB would trip in the required time.

Using an RCD does not replace the need for low (R1 + R2) values, but does mitigate the higher Ze readings.
 
Last edited:
engineer54 I have always thought a tncs system worked your way but as i have never worked beyond an installation ie in the network so have not had any experience of working with to many differnt systems. When I started my new job working along side generators two sparks there explained to me that an earth rod was not always needed on a tncs system. I did question this but eager not to look unexperienced and as they both had experience in this field and also ship wiring which uses no earth rod, I assumed I had miss understood the system. Since you pulled my comment i have found as many sources of information as I can and educated myself reguarding tncs sytems. I am happy to have been wrong as otherwise I would still be non the wiser. I have explained to these sparks and concluded that they some how had the IT system for ships and a TNCS system mixed up and that a source of earth was always required for a TNCS. Reguarding the generators most already come with a neutal earth link inside with a label on the front stating this. All the generators have rods installed, it was just the fact I was told that if removed the ocpd would still work fine, which we can safely say I know now to be wrong. Anyway thanks for pulling my comment and I think ill keep my advice to myself unless 100% sure next time, oh well
 
Well we have both learnt something from this thread then...lol I now know that marine electrical systems, use an insulated neutral arrangement...lol!!

Always better to ask questions, or ask to confirm your understanding of things, than keeping quite. Nothing stopping you giving advise on these forums, if your wrong you'll get someone here that can correct you, ...just another way of learning and picking up things!!
 
Robbie what is the trip rating in mA of the RCD part of your RCBO ?

The max Zs values for RCD's RCBO's depend on the mA rating, and are as follows:

30mA = 1667 ohms
100mA = 500 ohms
300mA = 167 ohms
500mA = 100 ohms

So your Zs values will be fine


The OCP part requires more thought, as your Ze values are low, it is the (R1 +R2) values which are giving the higher part of your readings.

If it is a TN system and a distribution circuit, a 5 second disconnection time will be allowed.

As a 25 A C type OCPD will require 250 A to operate instantaneously, 10 X 25A , 230/250 = 0.92 ohms, but if you are allowed a disconnection time of 5 secs this can be higher.

Edit; I have not included any correction factors here for clarity
 
Last edited:
This is a boat and is outside the scope of BS7671 - think you need to consult a grown up.

As a previous poster has mentioned you need to have fault monitoring devices installed.
 
Until we know the precise method of “earthing” the generator neutral it’s like trying to plat fog.

Totally impossible.

You keep prevaricating around the questions, which leads me to think you’re in the mire over your head.

I’ll PM Durham
 
hehehe!! im in no position to give advice to the un advisable!

on a water based craft we had NO earth and tbh EFLI and RCD's we unheard of in the RN..!
yes we had a constant IR monitoring system checking for Earth Faults to the Hull of the ship..! our limit was under 600k ohms then we had to investigate, on a good day 999m ohms was achievable but seen as our MG sets used to eat carbon brushes for dinner it soon dropped rapidly! out come the Air guns and rags!! on completion it seemed like scene from marry poppins and the chimney sweeps..!


any way back to the point...! do you have a Neutral Earth TX at the generator? to assist with fault current when starting up and running etc..?
 
You need a marine engineering consultant, this area is a minefield and there's many variables you need to consider before designing this kind of system. The system needs to consider safety of people on the barge as well as people not on the barge primarily but corrosion implications can cost astronomical amounts if not considered correctly.

I'm not an expert in this field but the marine projects I have been involved in have taught me you can't cut corners.
 

Reply to generators in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

We’ve recently completed the first and second fix of a barn conversion that is off grid with solar PV, batteries and a back up generator. This...
Replies
0
Views
190
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
555
  • Question
Thanks westward great advice as always 👍
Replies
14
Views
2K
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
562
loz2754
L
  • Question
Thank you for the info. I will make sure he is aware of what’s required for him to do before switching over to it. Thanks again
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks