Hi,

My hot tub keeps tripping after 12 years of use. I'm thinking it's the GFCI gone bad. Unfortunately it's a CH 2 pole 50 amp (GFTCB250) and they are on national backorder. The only options I can think of are to put a GFCI in the main panel (Sqaure D) and replace the GFCI at the disconnect with a standard breaker but I'm not sure if that can be done. The other option is to replace the entire disconnect with a new one that has a GFCI. Perhaps something is wrong with the hottub as well but everything had been working until we switched the breaker off to drain the tub. Any thoughts on what can be done?

TIA.
 
It may not be the gfci. Don’t rule it out though.

Do you have equipment for testing the unit? Do they come with a test button like RCDs in the Uk?
We also have professional test equipment that not only tests that an rcd trips within it’s time limit (standard 40ms) and can also test the threshold of earth fault that it trips at. (A 30mA device can trip at a lot less… ie 20mA)

It may be the tub itself, in which case, the gfci is doing exactly what it’s meant to; cutting off the power so nobody takes a dip in sparkling water. :(

Do not, under any circumstances, run it without a gfci present.

In UK, my house has 30mA rcd on all socket outlets, and a further 10mA built into the flex for the tub. Double protection.
 

Reply to GFCI for hot tub keeps tripping in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
703

Similar threads

  • Question
It sounds like there is damage to the wiring underground. Do you know what kind of cable was used, in any underground wiring is used has to be UF...
Replies
3
Views
640
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top