I have a nominal 4Kw system comprised of 16 REY solar panels arranged on my roof with 11 facing south east and 5 facing south west.
it is now 11.15 am and the Gfi (Ground fault indicator) LED is still illuminated. The total generation (FIT) meter is showing a red light which means that no power is being fed into the grid (the same as at night time). I am now going up into the loft to attempt to restart the system and photograph the Aurora Power One (model 3.6) Inverter screen whilst it is still displaying the fault message.
OK, I have now completed my observations and they are as follows:
When I first looked at the fault message on the screen it read “Measuring riso (see attached image)”. This message stayed on screen with the salt timer icon revolving continuously.
I then turned off the two individual panel strings and waited for the Inverter to turn off. I then turned on the 1st string (facing south east) and it eventually showed a message which read “Riso low” which settled down to a reading of 0.60 M (see attached image). The fault message remained on the screen and pressing the “Esc” button only illuminated the screen and did nothing else.
I then turned off the 1st string and waited for the inverter to turn off. I then turned on the second string (facing south west) which started up normally with a Riso measurement of 20 M (normal). Whilst this was still operating I turned on the first string and that too started up normally with both panel strings showing a good output of 1750w and 700w respectively.
I then turned off both strings and waited for the inverter to turn off and restarted both strings simultaneously with the result that the original Gfi fault showed and the “Riso low” message displayed. I turned off the two strings and once again started them up consecutively by first turning on the 2nd string (facing south west) until it showed me the normal Riso of 20 M and outputting around 700w then turning on the 1st string (facing south east) which also now started up normally with an output of 1750w. This is how I have now left the system.
The temperature reading on the inverter was 12.5C when first observed and 14C when I last observed it.
What is the most likely cause of this GI fault?
Shaun
it is now 11.15 am and the Gfi (Ground fault indicator) LED is still illuminated. The total generation (FIT) meter is showing a red light which means that no power is being fed into the grid (the same as at night time). I am now going up into the loft to attempt to restart the system and photograph the Aurora Power One (model 3.6) Inverter screen whilst it is still displaying the fault message.
OK, I have now completed my observations and they are as follows:
When I first looked at the fault message on the screen it read “Measuring riso (see attached image)”. This message stayed on screen with the salt timer icon revolving continuously.
I then turned off the two individual panel strings and waited for the Inverter to turn off. I then turned on the 1st string (facing south east) and it eventually showed a message which read “Riso low” which settled down to a reading of 0.60 M (see attached image). The fault message remained on the screen and pressing the “Esc” button only illuminated the screen and did nothing else.
I then turned off the 1st string and waited for the inverter to turn off. I then turned on the second string (facing south west) which started up normally with a Riso measurement of 20 M (normal). Whilst this was still operating I turned on the first string and that too started up normally with both panel strings showing a good output of 1750w and 700w respectively.
I then turned off both strings and waited for the inverter to turn off and restarted both strings simultaneously with the result that the original Gfi fault showed and the “Riso low” message displayed. I turned off the two strings and once again started them up consecutively by first turning on the 2nd string (facing south west) until it showed me the normal Riso of 20 M and outputting around 700w then turning on the 1st string (facing south east) which also now started up normally with an output of 1750w. This is how I have now left the system.
The temperature reading on the inverter was 12.5C when first observed and 14C when I last observed it.
What is the most likely cause of this GI fault?
Shaun