Glanding 3 phase into metal distribution board. | on ElectriciansForums

Discuss Glanding 3 phase into metal distribution board. in the UK Electrical Forum area at ElectriciansForums.net

-Matt

-
Joined
Jul 27, 2015
Messages
116
Reaction score
157
Location
England
Quick question, have a small caravan site to wire up.

Have 3 phase supply and TT earthing, 30ma RCD in each individual pods.

Was planning on using a 100ma type S incomer in the main DB to protect the sub feeds. ( this should stop a dodgy caravan tripping the whole site being 100ma time delay).

However not overly familiar with TT and 3 phase in terms of protecting the tails.

Ive been told by my niceic assessor with single phase and metal consumer unit, it is fine to just use the special stuffing glands.

However i dont think they make them for 3 phase?

So how would you do this?

Or would it be best to just get a seperate insulated board to house the RCD and then main switch in the DB?

Anyone any advice on this?
 
The tails should be wired via the load side of the S type rcd within a separate insulated enclosure hence will have fault protection to them when they enter the 3 phase DB.
Take them through a suitable entry protecting against sharp edges like a bush and locknut combo or something similar.
 
The tails should be wired via the load side of the S type rcd within a separate insulated enclosure hence will have fault protection to them when they enter the 3 phase DB.
Take them through a suitable entry protecting against sharp edges like a bush and locknut combo or something similar.
But not in seperate holes for each phase
 
If an electrician is installing if,Who would do such a thing?
Ian I have seen "Electricians" do exactly what I warned against, you often get poorly trained guys doing it, I was helping my Son do an alarm system in a barn, brought all 4 tails into the enclosure in seperate holes, he was there working, well you must know me by now I couldnt keep my gob shut, had to tell him, got told to Fox Trot Oscar. Don't know what the outcome was, the barn is still there though.
 
Thanks guys, upfront plastic box it is then, was just hoping to simplify slightly by having it all in one box.

And yes all tails will enter through one brass bush.
( i have however come across a fair amount of new domestic boards where the tails come through separate glands! even with single phase I'm pretty sure this is a NONO!)
 
Thanks guys, upfront plastic box it is then, was just hoping to simplify slightly by having it all in one box.

And yes all tails will enter through one brass bush.
( i have however come across a fair amount of new domestic boards where the tails come through separate glands! even with single phase I'm pretty sure this is a NONO!)
Yeah it’s a no no and I bet there’s countless DBs where the tails enter the DB without protection against abrasion.
 
Ian I have seen "Electricians" do exactly what I warned against, you often get poorly trained guys doing it, I was helping my Son do an alarm system in a barn, brought all 4 tails into the enclosure in seperate holes, he was there working, well you must know me by now I couldnt keep my gob shut, had to tell him, got told to Fox Trot Oscar. Don't know what the outcome was, the barn is still there though.
I told the customer that the sparky had done it wrong and then he paid me to do it properly
By the way you can bring it in separate glands if you slot the metal dB
 
I told the customer that the sparky had done it wrong and then he paid me to do it properly
By the way you can bring it in separate glands if you slot the metal dB
And the dipstick that ordered the Electrician runs his own business, going wrong somewhere Mate, you think????? Seems the less you know the more money you make, the dipstick.
 
Ref posts 8 & 9, as long as the locknut used on the glands is also brass/non-ferrous as many glands come with a steel locknut.
Must disagree there Steve, wht's to stop the steel of the gland by passing the brass gland, scientifically correct but practical? no chance.
 
If you are slotting a steel enclosure to enable phases to enter through separate routes, whether by bush gland or whatever, if you use a steel locknut then you have negated the point of slotting the steel plate in the first place, as you will be magnetically bridging the slot from either side. Where slots are made for this purpose then brass fittings - either side, would be favourite.
 
If you are slotting a steel enclosure to enable phases to enter through separate routes, whether by bush gland or whatever, if you use a steel locknut then you have negated the point of slotting the steel plate in the first place, as you will be magnetically bridging the slot from either side. Where slots are made for this purpose then brass fittings - either side, would be favourite.
Steve, I respect your thoughts, but disagree, experience tells me, although theoretically it works, practically and experience tells me it's a No, sorry Mate.
 

Reply to Glanding 3 phase into metal distribution board. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
712
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top