haven't got attitude. don't see why people can't share information. we are here for a good time. not a long time.And with that attitude your not going to get very far are you mate.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Glass washing machine 3 phase 63a per phase in the Commercial Electrical Advice area at ElectriciansForums.net
haven't got attitude. don't see why people can't share information. we are here for a good time. not a long time.And with that attitude your not going to get very far are you mate.
Grow a pair Joey.i haven't no. its easier to ask. but as i guessed on here its a waste of time. I'm extremely tired. earnt ÂŁ1630, in 4 days and working tomorrow. but yes I'm a useless **** yes yes. came on here for advice.
Don't get your knickers in a twist.......go and count your dosh and go to bed.i haven't no. its easier to ask. but as i guessed on here its a waste of time. I'm extremely tired. earnt ÂŁ1630, in 4 days and working tomorrow. but yes I'm a useless **** yes yes. came on here for advice.
haven't got attitude. don't see why people can't share information. we are here for a good time. not a long time.And with that attitude your not going to get very far are you mate.
yes i have done cable calcs to determine cable size. but unsure if a fused isolator was nessasary? it seems not? and my theory of running a separate cpc is also not nessasary??I think it is quite a jump from domestic/new build to go into commercial and do a 3 phase but in principle I cannot see why anyone should not do so. The tech department who does the machine should be able to advise. Is there any reason someone should not be helped or encouraged on such a jump really? It seems the basic calcs are done and yes there would appear to be a learning curve involved but are we not here to do that??? or no? Or am I missing something?
what size of cable ?answer on a post card .to top dog electrical forums .via father xmas north pole .the worldso straight off of a 63a three phase crabtree breaker to a commando socket?
try 10mm cable.Commando socket serves as local Isolation so it's fine.
However,
Personally I'd come from the DB to a 125amp rotary Isolator then link with a bit of 25mm conduit and mount the plug underneath, or I'd get a socket with a built in isolator.
The reason I'd go this route is because your struggle terminating an 16mm 4 core SWA straight into a 63 amp socket.
In my opinion 63amp rotary isolators are made to small as well
Volt drop too high though on 45m. hence 16mm²?10mm cable.