glitch in Power One 3.6 OUTD power reporting? | on ElectriciansForums

Discuss glitch in Power One 3.6 OUTD power reporting? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

S

Sunshine777

Every now and then my system with a Power One 3.6 OUTD inverter reports a cumulative power output for the day of 255 watts even though it's only just turned on at perhaps 08:00 and the actual instantaneous output is perhaps in the single figures or low double figures. Thus 255 Wh for the day so far is rather implausible. A check on the live output page on pvoutput at the same time reveals perhaps 1, 2 or 3 systems every day with early morning outputs at or above 255 Wh while the rest are at just a few watt hours. Check their inverters and every time it's a Power One 3.6 OUTD. Drill down into the daily page for each system and again the cumulative vs instantaneous outputs don't correlate. I suppose it doesn't matter much in the greater scheme of things as the inverter's power reporting is just for informational purposes and its the only generation meter reading that really matters but curious if others have seen this or have an explanation.

Here's a snapshot from pvoutput from this morning; the first 3 systems all have Power One 3.6 OUTD inverters:
Live Outputs
RankIntraday LocationSystem SizeEnergyEfficiencyPowerSeenAwakeUpdatedOnline
[ElectriciansForums.net] glitch in Power One 3.6 OUTD power reporting?
1BlackBoys United Kingdom TN223.760kW0.404kWh0.107kWh/kW265W3 mins ago00:0008:308hr 30min

2Uncle Mike Dundee United Kingdom DD53.760kW0.265kWh0.070kWh/kW70W31 secs ago07:5508:3540min

3Dunfermline SSE+WSW Arrays United Kingdom KY123.675kW0.255kWh0.069kWh/kW3W5 mins ago00:0008:308hr 30min
4KCHOME United Kingdom TN343.920kW0.215kWh0.055kWh/kW360W2 mins ago00:0008:308hr 30min
5Workshop United Kingdom DA19.890kW0.188kWh0.019kWh/kW264W40 secs ago07:4508:3045min

6St Lawrence Solar United Kingdom PO383.960kW0.138kWh0.035kWh/kW292W6 mins ago00:0008:308hr 30min

7JayEmmCeeOne United Kingdom RG274.080kW0.138kWh0.034kWh/kW168W5 mins ago07:2008:301hr 10min

8Gillingham Generator United Kingdom ME74.000kW0.124kWh0.031kWh/kW204W4 mins ago06:1508:302hr 15min

9PAD4U United Kingdom M193.840kW0.115kWh0.030kWh/kW216W8 mins ago00:0008:308hr 30min
10Maidstone-UK United Kingdom TN123.900kW0.113kWh0.029kWh/kW228W4 mins ago07:5008:3040min

11Purr Power United Kingdom PO153.760kW0.110kWh0.029kWh/kW192W2 mins ago08:0008:3030min
12MJB_HFW2 United Kingdom BN423.600kW0.108kWh0.030kWh/kW204W2 mins ago07:5508:3540min

 
No, just random mornings.

Same here - getting really annoying, sometimes it is a glitch of several kWh at start up.

I thought at first it was a communication error from the inverter to the computer (running Aurora Communicator), but the inverter display also shows the same wrong energy reading on the display for that day.

Here is a sample of part of today's log showing what is happening:

[info]
Plant Name:
Date: 19/04/2012


[measurements]
Time;Address;Model;MPPT;VDC1;IDC1;PDC1;VDC2;IDC2;PDC2;VAC;IAC;PAC;TINV;TINT;ENERGY;RISO;ILEAK;GENFREQ;
;;;;VDC;ADC;W;VDC;ADC;W;V;A;W;°C;°C;Wh;MOhm;mA;Hz;


[start]
05:47;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0;0;
05:48;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0;0;
05:49;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0;0;
05:50;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0;0;
05:51;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0;0;
05:52;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0;0;
05:53;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0.0;0;0;
05:54;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
05:55;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
05:56;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
05:57;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
05:58;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
05:59;2;PVI-3.6-OUTD-UK;D;0.0;0.0;0.0;91.7;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:00;2;PVI-3.6-OUTD-UK;D;101.9;0.0;0.0;110.4;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:01;2;PVI-3.6-OUTD-UK;D;101.9;0.0;0.0;110.4;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:02;2;PVI-3.6-OUTD-UK;D;122.1;0.0;0.0;110.4;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:03;2;PVI-3.6-OUTD-UK;D;122.1;0.0;0.0;110.4;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:04;2;PVI-3.6-OUTD-UK;D;122.1;0.0;0.0;110.4;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:05;2;PVI-3.6-OUTD-UK;D;104.9;0.0;0.0;123.8;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:06;2;PVI-3.6-OUTD-UK;D;104.9;0.0;0.0;123.8;0.0;0.0;0.0;0.0;0.0;0.0;0.0;2948.0;0.0;0;0;
06:07;2;PVI-3.6-OUTD-UK;D;93.4;0.0;0.0;92.5;0.0;0.0;245.8;0.0;0.0;9.4;9.4;2948.0;0.0;0;0;
06:08;2;PVI-3.6-OUTD-UK;D;193.9;0.0;0.0;193.8;0.0;0.0;245.3;0.0;0.0;9.6;9.5;2948.0;0.0;0;0;
06:09;2;PVI-3.6-OUTD-UK;D;179.8;0.0;0.0;175.9;0.0;0.0;245.3;0.0;0.0;9.8;10.1;2948.0;20.0;0;0;
06:10;2;PVI-3.6-OUTD-UK;D;172.4;0.0;0.0;196.1;0.0;0.0;245.1;0.0;0.0;9.9;10.5;2948.0;20.0;0;0;
06:11;2;PVI-3.6-OUTD-UK;D;204.7;0.0;0.0;202.6;0.0;0.0;245.5;0.0;0.0;10.0;10.9;2948.0;20.0;0;0;

See the 2948 (Wh) ? - that should not be there.

I have tried different Vstart1 and Vstart2 settings, but no difference. (I have 2 strings, 7 panels, 8 panels).

It looks like a surge or spike that is confusing the inverter? - I would think it might be possible to fix it in firmware, but I'm not aware of any way to get the firmware updated on the Power One.
 
I have spoken to power one about glitches with the desktop displays, we have a few which show totals on the statistics page that don't add up to the totals on the main page, they say they are aware of issue and we need to wait for a software update maybe this is a related problem.

On a separate note when you update the fit price you then get the income adjusting for everything you generated at the new rate making the figure irrelevant. Anyone know of a way to fix this?

Tom
 
is it anything to do with the capacitors discharging / charging?

It may be Gavin, but the firmware should be able to tell that the energy reading is spurious as it suddenly jumps up to a figure from nothing in an instant, yet the power is still zero. I suspect it may be some spike getting coupled into the measuring system.
 
I have spoken to power one about glitches with the desktop displays, we have a few which show totals on the statistics page that don't add up to the totals on the main page, they say they are aware of issue and we need to wait for a software update maybe this is a related problem.

On a separate note when you update the fit price you then get the income adjusting for everything you generated at the new rate making the figure irrelevant. Anyone know of a way to fix this?

Tom

I don't think it is possible to have different rates for different periods. PVOUTPUT does allow this though.
Now if only we could get rid of the glitch in Energy while starting up and the PVOUTPUT live results would be accurate.

I do have a desktop display as well, but only use it for quickly checking what is going on, it is extremely poorly designed, can't even keep the display on all the time, it goes to sleep. If I had known how poor it was I would not have bothered with it, as the combination of a dedicated PC running Aurora Communicator and uploading to PVOUTPUT and an iPhone is much better IMO.
 
I don't think it is possible to have different rates for different periods. PVOUTPUT does allow this though.
Now if only we could get rid of the glitch in Energy while starting up and the PVOUTPUT live results would be accurate.

I do have a desktop display as well, but only use it for quickly checking what is going on, it is extremely poorly designed, can't even keep the display on all the time, it goes to sleep. If I had known how poor it was I would not have bothered with it, as the combination of a dedicated PC running Aurora Communicator and uploading to PVOUTPUT and an iPhone is much better IMO.

I get he same issue already twice in 3 days !
 
[ElectriciansForums.net] glitch in Power One 3.6 OUTD power reporting?

See, it start at 12 KWh, wich is far too high
 
A customer of ours was reporting the same issue. He does not have a remote display but was getting impossible daily generation figures of 7.5kW by 08.15am etc. plus inconsistencies between weekly totals and the generation meter. Riased issue with Power One UK, they put me on to technical who confirmed that some older models installed around 6 months ago have a problem with the total generation amounts. They will arrange for a technician to visit the site and upgrade the firmware on completion of an online form. They emailed the link straight over and asked me to pass on to the client to complete.

Will let you know how quickly they organise the site visit but I was impressed by their customer service (unlike my experience with SMA :thumbs_down:)

Cheers

Monty
 
A customer of ours was reporting the same issue. He does not have a remote display but was getting impossible daily generation figures of 7.5kW by 08.15am etc. plus inconsistencies between weekly totals and the generation meter. Riased issue with Power One UK, they put me on to technical who confirmed that some older models installed around 6 months ago have a problem with the total generation amounts. They will arrange for a technician to visit the site and upgrade the firmware on completion of an online form. They emailed the link straight over and asked me to pass on to the client to complete.

Will let you know how quickly they organise the site visit but I was impressed by their customer service (unlike my experience with SMA :thumbs_down:)

Cheers

Monty

Same problem Today.

[ElectriciansForums.net] glitch in Power One 3.6 OUTD power reporting?
 
i contacted the power one support and they asked me to fill an excel sheet with details.
They have upgraded the firmware using their laptop. So far do good.
 
I have a pair of the same inverters and one of them started to display the daily generation error a couple of weeks ago. I contacted the installer (a large company) they say they have not heard of the problem! The inverters were installed in the early part of 2012.
Does anybody have a contact at power-one or a link to the online form to report the problem.

Many thanks
Jonesmabel
 

Reply to glitch in Power One 3.6 OUTD power reporting? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
134
  • Sticky
  • Article
Thank you for getting in touch! Looking forward to use your services in the future! :)
Replies
3
Views
474
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
409

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top