I shall be replacing my dual RCD CU, for a all RCBO populated CU. A question or two about technique for IR testing.

For the IR test, I've read here before that a global IR test is preferable. With older types of RCBO's that wasn't possible, without disconnecting cables, which ended up with the testing of each individual circuit.

I'm installing a Hager CU, with their miniature ADA RCBO. The MI state an IR test can be carried out on the RCBO terminals, circuit connected with the RCBO turned off. As I've a few different sorts of luminaire connected, I will be doing live/neutral to to earth.

How do you carry out such a test? I've seen some stackable MFT leads, so you can combine live & neutral together?
 
UK plug inflicts more pain to feet than any other, ergo it is best.

Joking aside, I find the heft of BS1363 plugs quite reassuring. The next best in terms of robustness (that I've encountered) would probably be Schuko, but no domestic plug mates as solidly with a socket as our 3 pin beast.
 
Last edited by a moderator:
UK plug inflicts more pain to feet than any other, ergo it is best.

Joking aside, I find the heft of BS1363 plugs quite reassuring. The next best in terms of robustness (that I've encountered) would probably be Schuko, but no domestic plug mates as solidly with a socket as our 3 pin beast.
Amen to that. That's why I describe the europlugs as "flimsy". Whereas the traditional 13amp 3 pin has very much a feel of "I won't let you down" about it.
 
Whereas the traditional 13amp 3 pin has very much a feel of "I won't let you down" about it.
When you stand on one it won't let you down to the floor, that is for sure!

I never seemed to suffer that, but as a child my sister had an uncanny knack of finding each and every plug that was ever left prongs-up. Perhaps she save me by her self-sacrifice! :)
 

Reply to Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top