Re: gs3 flaws
Fair comment,I should have used the word "little effect" on short circuit protection
In that a short circuit doesn't exist, where a resistance either a load or a high resistance connection is in circuit
In a double fault situation, your example is correct (where a L_N short and a loose neutral connection exist )
I suspect that the loose connection resistance of the neutral would in most circumstances,rise to such a point that the load resistance coupled with the loose connection resistance would stop current flow
As you rightly say, the second fault would affect the short circuit protection if it occured before the loaded circuit gave up the ghost