Eh up :)

Someone tell me where I'm going wrong.

I'm reading up on testing theory, using GN3 (6th edition, incorporating Amd 1, 2012). Section 2.7.7, pp40-41.

"Simple installations that contain no dist. ccts should pref be tested as a whole, see fig 2.4a."

[ElectriciansForums.net] GN3: IR test, whole installation vs final circuit

"Test should be carried out with main switch off, all fuses in place, switches and cct breakers closed, lamps removed..." blah blah.

Got it. All good :)

Next:

"Example (ii) - IR test of a final cct. Fig 2.4b shows an example of testing a single final circuit at a CU (only the line to neutral test is shown)."

[ElectriciansForums.net] GN3: IR test, whole installation vs final circuit

Unlike the first example (fig 2.4a, for the whole installation) there is no accompanying text to say, "main switch like this, fuses like that or CBs like the other," all you've got to go on is the picture.

But all the breakers are set to "on". Which means, all your circuits will be in parallel, wont they (as far as an IR test is concerned)? And you're not doing an IR of just one circuit at all, you're doing the whole installation again. Aren't you? Should you, in fact, turn the breakers off / remove the fuses (to IR test individual circuits)?

Or am I going wrong somewhere?

:)
 
looking at the 2 pics. the only difference is that the 2nd example is through the MCB so will also give a global reading. unless i'm missing something due to the beer.
 
Eh up :)

Someone tell me where I'm going wrong.

I'm reading up on testing theory, using GN3 (6th edition, incorporating Amd 1, 2012). Section 2.7.7, pp40-41.

"Simple installations that contain no dist. ccts should pref be tested as a whole, see fig 2.4a."

View attachment 26208

"Test should be carried out with main switch off, all fuses in place, switches and cct breakers closed, lamps removed..." blah blah.

Got it. All good :)

Next:

"Example (ii) - IR test of a final cct. Fig 2.4b shows an example of testing a single final circuit at a CU (only the line to neutral test is shown)."

View attachment 26209

Unlike the first example (fig 2.4a, for the whole installation) there is no accompanying text to say, "main switch like this, fuses like that or CBs like the other," all you've got to go on is the picture.

But all the breakers are set to "on". Which means, all your circuits will be in parallel, wont they (as far as an IR test is concerned)? And you're not doing an IR of just one circuit at all, you're doing the whole installation again. Aren't you? Should you, in fact, turn the breakers off / remove the fuses (to IR test individual circuits)?

Or am I going wrong somewhere?

:)

yeah you are right the breakers are still on and the cable is terminated into the breaker so it would just do a global line to neutral again with the illustrations its basically the same test, it should show the breaker off or to take the cables out of the terminals and test it by its self (that's what i do when test one circuit). its definatly interesting haha
 
Just looking at this in gn3 and if you look down to fig 2.4c page 42 it says when ir testing the armorings of swa the armorings need to have a connection to earth :/ i did not know that but usually when i have tested swa it is normally teminated to a metal board which is earthed so i suppose it is earthed any way.
 
Yeah, there's a bit of commentary about that (need to connect the protective conductor to the earthing arrangement when IR testing between the live conductors and the CPC) on P39. Apparently it's a change that came into effect with the 17th Edition in 2008.
 
Could this be to make sure cables have not been damaged during the installation process and still have sufficient insulation resistance values from the means of earthing and what is connected to it. Surely if a cable was tested disconnected from the MET then you are only testing to check the cable cores are all properly insulated from each-other and not that the live cores are separate from everything else connected to the means of earthing?
 
Could this be to make sure cables have not been damaged during the installation process and still have sufficient insulation resistance values from the means of earthing and what is connected to it. Surely if a cable was tested disconnected from the MET then you are only testing to check the cable cores are all properly insulated from each-other and not that the live cores are separate from everything else connected to the means of earthing?

I have ony just come in from pub and that is what i am thinking to make sure every core is not connected to earth by some means or another
 

Reply to GN3: IR test, whole installation vs final circuit in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top