I will speak to my tutor on Thursday evening as he says not, this needs clarifying as if he is wrong, he is teacher the wrong information. With regards to using a proving, below is the response I got from the NIC when asking them whether you can use the supply of the consumer unit as a known source for safe isolation procedure:
Thank you for contacting the NICEIC technical Helpdesk, in answer to your question, some voltage indicators have a self check facility, if you are using these there is no requirement for a proving unit (GS38), BUT if your indicator does not have a self check function, how would you confirm that the supply is dead, if you are working on an old installation with a possible dead supply entering the building (no live supply), your indicator will indicate no voltage, and this might be a blown fuse/faulty component within the indicator, giving the wrong indication and the resultant outcome could be fatal.
We have attached BPG 2 and GS38 for your information.
Regards
NICEIC Technical