When measuring Ze, R1+R2, polarity, etc, this is classed as testing procedures where the main fuse is allowed to be re-instated to power the consumer unit for testing purposes only. When removing the consumer unit front cover for the first time, the main fuse below must be taken out and isolated.
 
When measuring Ze, R1+R2, polarity, etc, this is classed as testing procedures where the main fuse is allowed to be re-instated to power the consumer unit for testing purposes only. When removing the consumer unit front cover for the first time, the main fuse below must be taken out and isolated.

Utter rubbish, on the 2391 practicle exam, the main isolator on the board had to be locked off and then the cover could be removed. You could then use the known source (ie incomming supply) to test your meter and check that isolation on the installation has been carried out correctly.
 
I had this same discussion at night college last week with my tutor regarding using the incoming supply to test voltage indicators and he said you can not remove the CU front cover until it has been totally isolated, as per EaWR regs. He also said that it is not advisable to use another source to test meters therefore a proving unit should be used. I also have an e-mail from the NIC saying the exact same thing.
 
I had this same discussion at night college last week with my tutor regarding using the incoming supply to test voltage indicators and he said you can not remove the CU front cover until it has been totally isolated, as per EaWR regs. He also said that it is not advisable to use another source to test meters therefore a proving unit should be used. I also have an e-mail from the NIC saying the exact same thing.

You better ask him how I managed to pass safe isolation on my 2391 exam then!! and my last ELECSA assesment
 
Last edited by a moderator:
You CAN remove the cover of the CU provided the main switch and all MCB's etc, are in the off position.

This would then enable the safe isolation test to be carried out either side of the main switch.
 
You CAN remove the cover of the CU provided the main switch and all MCB's etc, are in the off position.

This would then enable the safe isolation test to be carried out either side of the main switch.

Thank You Jason
 
I will speak to my tutor on Thursday evening as he says not, this needs clarifying as if he is wrong, he is teacher the wrong information. With regards to using a proving, below is the response I got from the NIC when asking them whether you can use the supply of the consumer unit as a known source for safe isolation procedure:

Thank you for contacting the NICEIC technical Helpdesk, in answer to your question, some voltage indicators have a self check facility, if you are using these there is no requirement for a proving unit (GS38), BUT if your indicator does not have a self check function, how would you confirm that the supply is dead, if you are working on an old installation with a possible dead supply entering the building (no live supply), your indicator will indicate no voltage, and this might be a blown fuse/faulty component within the indicator, giving the wrong indication and the resultant outcome could be fatal.

We have attached BPG 2 and GS38 for your information.



Regards

NICEIC Technical
 
When measuring Ze, R1+R2, polarity, etc, this is classed as testing procedures where the main fuse is allowed to be re-instated to power the consumer unit for testing purposes only. When removing the consumer unit front cover for the first time, the main fuse below must be taken out and isolated.

Wow - how things have changed. That used to be a dead test. Progress i guess ;)


Seriously tho, whilst i totally agree you need clarification on this point (& your tutor should be doing more to provide it) its often tickled me how some react to proving units. Am i still missing something? It appears the electrical contracting industry is split on this - mention such a contraption to some & they react like they`ve been asked to give a urine sample in the middle of Asda :confused: Why? Ask another & they`ll tell you they`ll use the live side of an incomer if they happen to have one on them :) if not then the P U sure as hell beats roaming around looking for one. & as said, up a ladder, nothing else but chance taking fits the bill.
I agree, they do seem OTT expensive but it potentially may save you or others from harm one day - so to me, whatever i paid for my Martindale pair was worth it.
 
Having to read some of the advise given to trainees by their tutors and scaremongering nonesense quoted of the NIC chap
Health and safety protocol has overtaken common sense to the point of frightening would be electricians from carrying out their trade safely

If the main switch is off,locked off,then cover removed,approved voltage tester used,correct procedure to prove live and prove dead,why mangle minds with this unhealthy crap
 

Reply to the thread, titled "good GS38 approved voltage tester" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top