C

Crosswire

1) Fan isolator switches?

2) Earthing metal downlight rings holding a GU10 lamp?

3) Cable clamps in chocboxes


If poss quote Reg No.

Thanks!
 
1) Yes, fan isolators required for local isolation.
2) No, probably an impossible task.
3) Yes, cable clamps in choc boxes required to stop cables from being pulled out.

Hope this answers your queries.
 
Number 1 is surely a reg
Number 2 I suppose depends on insulation class of fitting
Number 3 wouldn't have thought it was a reg

Sorry no reg numbers, my books buried in cobwebs
 
1. A nice old grey area (but good practice)
2. Don't waste your time (and the clients money)
3. Don't think so.


I'm sure others will comment. Let the debate continue!
 
Yes

Grey area, the metal casing of the fitting requires an earth i think and most will provide a CPC connection on the metal arm that attaches to the ring (usually with a screw) Im not sure if this is a requirement or good practice only, I've always done it if a connection is provided.

Finally Yes, I had this discussion with an NIC assessor and under 17th it is a requirement according to him.

Again no reg numbers as.... well it would mean looking and im enjoying a beer :-)
 
1) No, 100% sure.
2) No, 100% sure.
3) No, but would be needed if chocbox was joining a vertical cable.

Unless manufacturers instructions for whatever you're installing says otherwise
 
Last edited:
agree if cables are clipped and box is screwed down. was thinking more of a floating chocbox as in fitted to downlights.
 
just found the page you're on. only problem was your page was in the OSG and mine was in MAD magazine.
 
No need for local isolation as long as provision somewhere in the circuit for isolating and, if not local, keeping isolated (ie. lock off the mcb) for mechanical maintenance of fan blades.
No req for clamping cables in boxes although MF connectors do, along with cables being connected in a "maintenance free" way. (see other threads)
Metal downlights should be earthed unless double-insulated. If required, then there should be some connection for cpc. (check installation guide as what they say is a req)
 
Reg no?



I think that was kinda the point I was trying to make about Chocboxes needing cable restraints when joining vertical/unsupported cables.

We're on the same page I think mate :)


This is exactly the situation I'm in.

Myself and several other sparks are doing identical second fix flats on price. Out of 4 sparks I was the only one to use the cable clamps to secure the cables supplying Wago connections for GU10 metal downlights.

Took me me an hour longer than the other guys and they said I was mad.

I was pretty sure the 17th edition required secured cables, hence the move from JB's to chocboxes, but they had me doubting myself. Needed a second opinion.

Incidently the down lights came with a green /yellow flylead attached to the arm of the holder and terminated in a connector block next to the live and neutral. First time I have seen this but makes perfect sense.

We automatically earth all other 230v metal lights, so why should downlights be excepted?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Good Practise or Specific Requirement?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
42
Unsolved
--

Advert

Thread statistics

Created
Crosswire,
Last reply from
rick,
Replies
42
Views
4,347

Advert

TrueNAS JBOD Storage Server

Back
Top