sythai

-
Arms
Hi Guys

Recently finished a new build house, 2 levels/ 5 bed.
Wired AICO grade D LD2 system throughout.

LABC has come to sign off saying needs to be grade A system.
Havent got full details, just to chatted to builder (owner of property) on phone.

Did only think this was required on a domestic property when 3 levels+ and/ or HMO ?

Can someone help on this please ?

Thanks Sy
 
Does this just apply to new builds… or do same regs apply for a refurb also above 200 sq/meters? Thanks Sy
The rule must have been in place for some time, i remember coming across it on a farm house refurb with extension 15 years ago, property was only 2 floor house, but about 250 sqm so required a grade A system. Be interesting to see if its the architects fault or labc if it was or wasnt on the plans
 
Last edited by a moderator:
….. so outcome was!

Architect got on the case and floor space was recalculated using a ‘net’ value which subtracts all the internal walls. This brought it in under the 200msq

And all fine with grade D/ LD2.

Good news for everyone involved😉

(Existing LABC causing grief on all fronts has also been given the boot and new private BC brought in.)
 

Reply to the thread, titled "Grade A... fire detection/ domestic property !?" which is posted in Domestic Electrician Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top