Hi All

I have to quote for wiring out an attached extension which will be used as a Granny Annexe, this will contain a small kitchen area & shower room. If I use a Henley block at the cut-out and run a 16mm T&E cable via a Switched Fuse to a separate CU for the Annexe will I need to provide Bonding in the Annexe? as the Main Services I.E. Water & Gas are already bonded in the house.

It is a TNC-S system. Also will the 6mm CPC of the T&E be sufficient if connected to the MET to serve the Annexe.

Thank you

Regards Newpark7
 
You need to calculate the size of the CPC required as per one of the standard methods. Either calculate using the adiabatic equation, or use the table which says anything up to 16mm requires a cpc of equal size to the live conductors.

You may need to provide bonding, but then again you may not, you need to assess whether or not there are extraneous parts accessible.
 
I don't follow, who on earth would be installing unnecessarily oversized conductors? It would be unnecessary!
We can only assume that the 16mm has been calculated as the necessary size and therefore the cpc could be sized as 16mm in accordance with that table.
 
Last edited by a moderator:
i'd use 16mm SWA. 1. the cpc is then adequate. 2. it don't need RCD protection. also, if water and gas services come from the main house pipework, they're already bonde, provided there's no plastic in the water pipes between the house and annexe.
 
I don't follow, who on earth would be installing unnecessarily oversized conductors? It would be unnecessary!
Precisely but lots do - see number of post saying "I always replace tails with 25mm. when changing CU".

If this annexe is having an 80A supply then 16mm sub-main will be required.
However, if 60A switch-fuse is fitted then 10mm would be sufficient - and/or used for cpc sizing (if not calculated) and half of that (except TNC-S) for bonding.


We can only assume that the 16mm has been calculated as the necessary size and therefore the cpc could be sized as 16mm in accordance with that table.
We can but hope.


If as you suggest the 16mm is oversized unnecessarily then I suggest the bloke is an idiot and may want to consider a career change to something befitting someone of lesser intelligence, painting and decorating for example.
Can I quote you the next time it arises?
 
I don't follow, who on earth would be installing unnecessarily oversized conductors? It would be unnecessary!
We can only assume that the 16mm has been calculated as the necessary size and therefore the cpc could be sized as 16mm in accordance with that table.

If as you suggest the 16mm is oversized unnecessarily then I suggest the bloke is an idiot and may want to consider a career change to something befitting someone of lesser intelligence, painting and decorating for example.

* Unnecessary comment removed*
 
Last edited by a moderator:

Reply to Granny Annexe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
793
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
979

Similar threads

Agreed, i have a cabin in the woods, water heating and hob is via 19Kg propane bottles, lasts ages and space heating is via warm air heaters via...
Replies
11
Views
2K
  • Question
Normally you'd install either a fuse-switch or a switchfuse at the incoming supply position rather than a DB, this gives you some hope of...
Replies
10
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top