I have recently taken over in the IT side of a medium company and one of the things I have noticed is a terribly installed wall mounted Data cabinet.
I have spent the weekend sorting it all out so it all comes up to spec but wanted to clarify on some points.
It is currently mounted on the wall but has not been earthed.
Power is ran from a 13amp BS 1363 from the trunking below to a small UPS in the cab. The UPS then breaks out onto a BS1363 PDU within the cab which is for a number of smaller DC powered devices (12, 24 and 48v transformers).
There is also a number of network switches installed (max, 250W), this is all grounded to an earth bonding bar that I have installed into the rack.
My question is, what do I earth the bonding bar to? Would it be acceptable to earth it to the earth in the ring main running below the wall mounted cabinet?