We have a strange problem.
We have a wind turbine and obviously when the wind doesnt blow we have to import electricity.
However intermittently (on a monthly basis) we have import figures that are maybe three times what we would expect based on the maximum load we could generate.
So we have a maximum of 50kw of load and we use this twice a day (dairy farm) and this is made up of various single phase motors, water heaters, cooling compressors.
We wont use all 50kw at the same time but its clustered around milking times and roughly we use it for two hours at a time twice a day (four hours total although water heating happens before milking and cooling continues a little after milking
However half hourly data suggests that sometimes we are importing maybe 150kw (in a half hourly period)
The turbine produces at 690 v and feeds into the grid at 11kv via a transformer. Then the farm is fed through a transformer ( down to 415v from 690 ) i.e three phase although the motors are all single phase.
We cant make head or tail of it as apart from the load not matching the milking times the import is vastly more than we think we could ever use.
Any ideas ?
Thanks in advance
 
Are you saying that for the suspect half-hour periods, the metering is showing energy consumption of 75kWh for that period, as opposed to a peak power demand of 150kW occurring somewhere during that period? If so, and you've only got 50kW of load, and the timing doesn't even correspond to when most of that is operational, then it does seem to be a metering fault. Whose metering is producing these figures?
 
Thanks for reply
Just looking at import half hourly data for 4th feb this year HH01 says 104KWh and HH02 says 103 KWh.
I assume HH01 is the frst half hour period after midnight.
At midnight the only thing that should be running is a water heater with a 6kw immersion in it.
It is possible that the cooling compressors kicked in briefly and these two are rated at 3.7kw each.
The farm meter which meters all the farm uses whether from the turbine or import has been checked and is ok.
The import /export meter has not been checked and to be honest I am not sure who this meter belongs to. I presume the supplying company (which is Good Energy) but surely if the meter is faulty it should be consistent shouldnt it ?
We wonder if there is any fault condition on the transformer that could cause this intermittently.
 
Is the imported data definitely for a single half-hour period on one day? It isn't (for example) the accumulated consumption in HH01 for a number of days or weeks, as recorded on 4th Feb?
A metering fault is possible as is a transformer fault or massive earth leakage, but with those numbers you'd know it was happening. 104kWh in half an hour implies average consumption of 208kW, if that was being dumped into a fault it would draw attention to itself.
Most likely explanation is misinterpretation of the data, which can be confusing, or a metering problem. Either way a chat to your supplier should sort it out.
 
It’s not an accumulated figure.
I thought a fault of that magnitude would be obvious.
I will check figures and talk to supplier
Thanks
 
If I have the right picture in my mind, you have a 3 phase 11kV supply into a transformer (T1) which outputs 690V. The wind turbine is three phase at 690V and is connected to the output of T1.

Also connected to the 690V lines is transformer T2 which outputs 415V 3 phase. The 415V supplies the farm equipment.

I reckon, the farm meter which measures total consumption(C) is connected into the 415V lines.

In order to measure wind turbine generation there is a half-hourly meter either in the lines from the turbine - in which case the meter records generation(G). Or, the half-hourly meter is connected into the 690V from T1, in which case this meter reads import(I). HH01 and HH02 refer to two watthour meters (for the 2 meter method of power consumption in a 3 wire 3 phase supply), and so the total power is HH01 + HH02.

Your settlement(S), ie what you owe the DNO for the electricity they supplied is either S= C-G or S= I.

With this explanation it would not be surprising if you recorded high HH01 and HH02 if wind produced a lot of generation and HH meter was for generation. What is the power of the turbine? I suspect it is the first HH meter configuration you have installed ie: to record generation. Thus S = C-G.

PS: I think these meter only work for one direction of power flow which supports S=C-G

A diagram or pictures would be helpful to clarify the purposes of the meters.
 
Last edited:
You said the meter indicates anomalous import figures. This implies the figures are signed(ie +/-) for import/export. Maybe, the recorded import figures are ignored by Good energy since they are only interested in what the turbine generates.

Electrically, the turbine's alternator when connected to the incoming DNO mains can also motor as well as generate. When it motors it will import energy and run as a big fan. Whether the turbine motors or generates depends on the prevailing wind speed, the voltage difference between the mains and alternator, and fluctuations in wind speed ie: acceleration/deceleration of the rotating blades caused by the wind. The 11kV/690V may be rising in voltage as the network loads reduce or HV transformer taps are changed to such an extent that the alternator voltage is lower than it - thus it motors. This why wind turbines turn when there is no wind. Just some musings.

[ElectriciansForums.net] half hourly import
 
Last edited:
If I have the right picture in my mind, you have a 3 phase 11kV supply into a transformer (T1) which outputs 690V. The wind turbine is three phase at 690V and is connected to the output of T1.

Also connected to the 690V lines is transformer T2 which outputs 415V 3 phase. The 415V supplies the farm equipment.

I reckon, the farm meter which measures total consumption(C) is connected into the 415V lines.

In order to measure wind turbine generation there is a half-hourly meter either in the lines from the turbine - in which case the meter records generation(G). Or, the half-hourly meter is connected into the 690V from T1, in which case this meter reads import(I). HH01 and HH02 refer to two watthour meters (for the 2 meter method of power consumption in a 3 wire 3 phase supply), and so the total power is HH01 + HH02.

Your settlement(S), ie what you owe the DNO for the electricity they supplied is either S= C-G or S= I.

With this explanation it would not be surprising if you recorded high HH01 and HH02 if wind produced a lot of generation and HH meter was for generation. What is the power of the turbine? I suspect it is the first HH meter configuration you have installed ie: to record generation. Thus S = C-G.

PS: I think these meter only work for one direction of power flow which supports S=C-G

A diagram or pictures would be helpful to clarify the purposes of the meters.

Aha !
I have discovered that the half hourly data I was furnished with as import is in fact export which rather makes sense of the numbers.( a bit of an elementary blunder methinks !)
Nevertheless we do still get intermittent months of high import just not as high as the figures I had suggested.
I have got the right data now so I need to look carefully at it before going any further.
Thanks anyway for your input. I may be back(having double checked I am talking sense )
 




Gilchrist: I turned up a few papers on electricity tariffs for dairy farms - there are many others. If your electricity usage is known hour by hour, day by day, you can see if a restricted time tariff might be more economical. Electricity suppliers are using so-called smart meters to encourage folk and businesses to 'even out' the peaks and troughs of demand by variable pricing eg: higher during peak times and much lower during surplus times, and also to reduce their own peak demand to avoid having to invest to in their infrastructure to provide more capacity. There are energy consultants if you don't feel like doing the research yourself but I would presume that like-minded farmers already have a wealth of advice to offer - see farming forum link.

:)
 
I thought a fault of that magnitude would be obvious.

This is sound logic that many people overlook. You would find it located somewhere near the red truck with flashing blue lights, approximately where the hoses are pointing. 200kW gets very hot very quickly.

Glad you have an explanation for the numbers so far...
 
You said the meter indicates anomalous import figures. This implies the figures are signed(ie +/-) for import/export. Maybe, the recorded import figures are ignored by Good energy since they are only interested in what the turbine generates.

Electrically, the turbine's alternator when connected to the incoming DNO mains can also motor as well as generate. When it motors it will import energy and run as a big fan. Whether the turbine motors or generates depends on the prevailing wind speed, the voltage difference between the mains and alternator, and fluctuations in wind speed ie: acceleration/deceleration of the rotating blades caused by the wind. The 11kV/690V may be rising in voltage as the network loads reduce or HV transformer taps are changed to such an extent that the alternator voltage is lower than it - thus it motors. This why wind turbines turn when there is no wind. Just some musings.

View attachment 50354
This is interesting. I am told categorically that turbines can not create a load. ( motor ?)
How certain are you of this ?
What might the expected consumption be if it can motor ?
I presume it’s related to turbine capacity.
This turbine is rated at 225 kw
 
Re #11: I admit I have assumed they were motoring when there was no wind or below the cut-in speed and the rotor was turning. I could not see how they could rotate without them drawing power. I'll do some more research and contact the renewable technology college in my home town to see what I can find out.
 
I have asked a university professor at a top university about energy consumption of wind turbines. Meanwhile, I turned this up - I caution it is from a site biased against wind but the remarks made are true enough about how a large wind turbine draws energy from the grid. What matters is the net contribution of energy to the grid by the turbine. You will read that the alternator does sometimes motor and draw power from the grid for a number of reasons including preserving bearings and preventing blade distortion.


It's why I asked were the HH meter was connected - in the lines from the WT or the lines from the secondary of the 11kV/690V transformer.
 
If the renewable metering is the same as for my friend's solar PV generation, he has two meters - one for actual total consumption in his household which he pays for at one rate/tariff say 15 p per kWh to his supplier say ScotPower; and another meter for what he feeds into the mains from his solar which he earns money from at another rate/tariff say 11 p per kWh.

In your case you do have a bill from an energy supplier for your actual total consumption on the farm and a payment from Green Energy for what you generate?
 
And one last thought for today - there are electrical network stability reasons why the DNO is not that bothered the turbine is connected and motoring, especially if the motoring power is small compared with the generating power. I suspect (can't say without more information) that watthour meters only record for flows in one direction so only generation is recorded not motoring. Whoever said the WT cannot create a load was imprecise; he should have a said it can be a load whose consumption is not recorded by the HH meter.

Anyway something for you to delve into.
 

Reply to half hourly import in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
753

Similar threads

Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
422
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top