Hi Guys

After bit of advice please....

Called back to kitchen job today, Hamilton light switch we fitted has burnt out?!
Normally decent gear so just trying to make sure nothing we have done (as Client not so friendly on this one.)

Switch in question is powering all the feature lighting which consists of:

4x75watt (240watts being used) & 1x40watt (30watts being used)/ 24v drivers running various LED cabinet lights.

Trying to check back spec of drivers can only find data sheet for 100watt version so be less than this:
Input 1.2amps so well under 10amp rating of switch and even before that it's on own 6a rcbo (new db installed) which would trip if overloaded.
But on spec sheet has inrush current <15amps, could this be causing the prob ? Not something I'm so familiar with being honest.

Hoping it's just the switch

Thanks Sy
[ElectriciansForums.net] Hamilton switch... burnt out !
 
I would remove the yellow cover .Would give more detail . Never had ONE issue with hamiltons .Very nice gear
same here.. decent stuff used for yonks !

I'm going to send back as less than 12months old and was bespoke item cost £25.
so don't really want to pull part and not be able to get back together... if you know what I mean.
 
Is it just me or does the C and E marking look very close together?

Dodgy copies???

Not saying it is, but maybe worth a check.

Edit.

Added photo.

This is what I’ve got to hand… oral B electric toothbrush. CE mark looks to have a space between.

View attachment 106887
hamiltons have both CE markings (narrow and apart) spread across their range .
 
I'd be very surprised if an instantaneous theoretical 15A inrush would cause that amount of damage - has it failed open or closed? There must be hundreds of thousands of 10A switches interrupting LED drivers up and down the land without issue, why should this one be any different?

I would be sending it back to Hamiltons for an inspection under warranty to see what they have to say.
 
I'd be very surprised if an instantaneous theoretical 15A inrush would cause that amount of damage - has it failed open or closed? There must be hundreds of thousands of 10A switches interrupting LED drivers up and down the land without issue, why should this one be any different?

I would be sending it back to Hamiltons for an inspection under warranty to see what they have to say.
failed open.... it's going back to Hamilton, see what the outcome is
 
The melted plastic alongside the switch mechanism, suggests that the heat came from the contacts, not the wiring terminals. High resistance or arcing could be caused by lack of pressure e.g. something mechanically broken, jammed or dirty, or faulty manufacture of the contacts themselves. I agree it's not likely to be caused directly by inrush, only by the continuous load. Excessive inrush can cause contact wear and damage and in time lead to failure, but not immediately. The switch is rated 10AX which means it doesn't need derating for inductive fluorescent / discharge lamp loads. LED drivers are not inductive so it's not directly comparable but it does mean the contacts are designed with inrush durability in mind.

Re. the CE mark, that is not the correct form and I too would be put on guard by a product from a reputable manufacturer with an incorrect marking. If the C is made into a complete circle it should just overlay the nearest side of the E. Non-standard marks like this have sometimes been used on non-compliant products and passed off as a different 'China Export' mark which is a scam.
 
The melted plastic alongside the switch mechanism, suggests that the heat came from the contacts, not the wiring terminals. High resistance or arcing could be caused by lack of pressure e.g. something mechanically broken, jammed or dirty, or faulty manufacture of the contacts themselves. I agree it's not likely to be caused directly by inrush, only by the continuous load. Excessive inrush can cause contact wear and damage and in time lead to failure, but not immediately. The switch is rated 10AX which means it doesn't need derating for inductive fluorescent / discharge lamp loads. LED drivers are not inductive so it's not directly comparable but it does mean the contacts are designed with inrush durability in mind.

Re. the CE mark, that is not the correct form and I too would be put on guard by a product from a reputable manufacturer with an incorrect marking. If the C is made into a complete circle it should just overlay the nearest side of the E. Non-standard marks like this have sometimes been used on non-compliant products and passed off as a different 'China Export' mark which is a scam.
Thanks Lucien very helpful and informative of you 🤩
 





Both types shown
 
Found this page.


There is also a Uk gov page that links out to a European site, but doesn’t show both CE marks
 

Reply to Hamilton switch... burnt out ! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
576
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
764
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top