This thread titled "Hardwiring an induction hob" is posted in the under the UK Electrical Forum on Electricians Forums.
I wouldnt wire the hob direct to kitchen circuit even if it comes with a plug as the regs advises against this but its rather vague ,just states cookers ,hobs and ovens should be on its own dedicated circuit unless less than 2 kw .its just trying to reduce the amount of load through your sockets.if it was a portable 2.9 kw hob then you could plug it in anywhere so it's not very clear in my opinion although I have stuck to it as good practice.you are allowed to apply diversity to your cooker circuit as the elements switch on and off at different times frequentlyI already have a 3kw double oven hardwired with 6mm twin and earth, direct to the consumer unit. Can I also add a 2.7kw hob to the same circuit?
Alternatively, can the hob be hardwired to the kitchen circuit?
I already have a 3kw double oven hardwired with 6mm twin and earth, direct to the consumer unit. Can I also add a 2.7kw hob to the same circuit?
Alternatively, can the hob be hardwired to the kitchen circuit?
I already have a 3kw double oven hardwired with 6mm twin and earth, direct to the consumer unit. Can I also add a 2.7kw hob to the same circuit?
Alternatively, can the hob be hardwired to the kitchen circuit?
Yeh that would def don't take it of sockets lol.you could possibly still be ok .the diversity could still be ok but the size of breaker would need to stay at 32 amps unless you know exactly how cable is run through the fabric of your house.it could be buried in 3 feet of glass wool or be a particularly long runI just realised that the hob power is 7,400 watts. Does that make a difference?
Is this an induction hob ?I just realised that the hob power is 7,400 watts. Does that make a difference?
Also some ovens will give the total load but that can never be reached as you can't have the grill and oven on at same time but would depend on model .mine is 3.4 kw but using clamp metre dosnt get anywhere near that regardless of what setting its onHow did it go from 2.7 to 7.4kW?
The 7.4 is the absolute maximum…. For hobs, we apply diversity as not all 4 rings will be on at the same time.
Reply to the thread, titled "Hardwiring an induction hob" which is posted in the under the UK Electrical Forum on Electricians Forums.