I have a property that was built (barn conversion) in 2008. I have the corresponding electrical inspection certificate dated 10-Jul-08, which states performed in accordance with BS7671 2001, amended to March 2004.

I since had an inspection in 2014 with no issues reported.

I have recently had an inspection and have been failed (C2 category, 5.12.1, & 2, & 3), quote…“absence of 30mA RCD protection to all circuits excluding DB1, SP12. The 30mA RCD protection was not raised on report in 2014 and should have been.”

So I have two reports that have not flagged RCD protection as a problem until the most recent, and I am now expected to pay a significant sum to correct this apparent “fail” when this is how the installation was performed and presumably signed off by a competent person, which I am obviously confused and upset about.

Questions
  • Was the installation and first inspection performed correctly in 2008?
  • What documents would I need determine specification stated in the planning approval?
  • If not, do I have any recourse with the builder or electrical company that did the initial installation in 2008?
  • Should the most recent inspection have been flagged as “fail” based on the information provided here?
Appreciate any advice you can offer

Thanks
 
An EICR is not a pass or a fail.... its a report that gives a satisfactory, or unsatisfactory outcome on how safe it is for continued use.

You do not have to use the same company that tested it do the remedial work.

5.12 on the report covers the need for rcd protection on 1. All socket outlets.... 2. For supply to mobile equipment to be used outdoors.... and 3. Cables concealed in wall buried less than 50mm deep.
If they were being this pedantic, they should have listed 5. All circuits supplying luminaires... as well

If there was no RCD installed in the first place, then I would report a C3, improvement recommended.
If there is an RCD, but it doesnt work properly.... then that is a C2, potentially dangerous.

Ultimately, its down to the testing engineer on the day and how strict they might want to report something.
A page full of observations could all be wiped out with one job of replacing a few circuit breakers with RCBOs.... or if the installation is in such a state of disrepair.... it might be the only way to convince the customer to upgrade.

There are unscrupulous individuals who may exagerate the problems somewhat to get the job of repair, but as i say above... you dont need to use the same company.... in fact, get a few quotes for the remedials.


There is a thought that if the property was to be rented out to a tenant, then duty of care would insist on RCD protection throughout.... safest possible.
 
Hi, and thank you for the quick reply. Comments much appreciated

Yes, I should have been more specific, it is “unsatisfactory”. However, in terms of my house insurance, it is a fail, as I will not be able to obtain house insurance without a “satisfactory” report. We are in the process of selling, and don’t wish to spend money upgrading unless it is required by law. If there is clear guidance on this, then it removes the opportunity for unscrupulous tradesmen to profit from a situation that they create.

So I guess my question is whether the electrician performing the inspection is governed by the regulations and should report C2 or C3 in this case where it is an existing installation with two satisfactory reports?
 
I have a property that was built (barn conversion) in 2008. I have the corresponding electrical inspection certificate dated 10-Jul-08, which states performed in accordance with BS7671 2001, amended to March 2004.

I since had an inspection in 2014 with no issues reported.

I have recently had an inspection and have been failed (C2 category, 5.12.1, & 2, & 3), quote…“absence of 30mA RCD protection to all circuits excluding DB1, SP12. The 30mA RCD protection was not raised on report in 2014 and should have been.”

So I have two reports that have not flagged RCD protection as a problem until the most recent, and I am now expected to pay a significant sum to correct this apparent “fail” when this is how the installation was performed and presumably signed off by a competent person, which I am obviously confused and upset about.

Questions
  • Was the installation and first inspection performed correctly in 2008?
  • What documents would I need determine specification stated in the planning approval?
  • If not, do I have any recourse with the builder or electrical company that did the initial installation in 2008?
  • Should the most recent inspection have been flagged as “fail” based on the information provided here?
Appreciate any advice you can offer

Thanks

Was the work started before the 1st July 2008? If so then the fail for "absence of 30mA RCD protection to all circuits excluding DB1, SP12" is incorrect. Up until 1st July 2008 designers could install to either the 16th or 17th Edition of BS 7671.

There might be sockets without RCD protection that may be used by outdoor equipment that should be addressed though.
 
Hi
I'm pretty certain the installation was done prior to July 2008, as the first certificate is a "certificate of installation" not a "condition report". I have planning documents that i downloaded dated 2007, so I believe July 2008 was when it was completed.

Reviewed my notes, and I was told that after 01-Jul-08, "Part P" was in effect (which I presume e must be 15th edition) and all cables needed 30mA RCD protection, and that if it was after Jul-08 the installation cert should of been to installed to 16th edition. That doesn’t sound correct to me, as that suggests you would perform an installation prior to 01-Jul-08 to one edition, and if not completed, be obliged to start again.

So if I go back to this company now, are they obliged to provide a satisfactory report, and if they refuse, do I have recourse to talk to the regulator that they are governed by? I think it’s NICEIC they told me

thanks
 
Hi
I'm pretty certain the installation was done prior to July 2008, as the first certificate is a "certificate of installation" not a "condition report". I have planning documents that i downloaded dated 2007, so I believe July 2008 was when it was completed.

Yes I understood that. That was dated the 10th July but the key is if the work was started before the 1st July. You seem to have documentation that shows it was started before 1st July so the C3 for this maybe incorrect if that is the case.
Reviewed my notes, and I was told that after 01-Jul-08, "Part P" was in effect (which I presume e must be 15th edition) and all cables needed 30mA RCD protection, and that if it was after Jul-08 the installation cert should of been to

Part P came into effect in 2005. All circuits ( in Dwellings) requiring RCD protection came in on the 17th Edition of BS7671 which came fully into effect on the 1st July 2008. The previous Edition was the 16th which didn't have this requirement.
installed to 16th edition. That doesn’t sound correct to me, as that suggests you would perform an installation prior to 01-Jul-08 to one edition, and if not completed, be obliged to start again.

Correct but because your Installation Certificate was dated the 10th July it opened up the possibility work started after 1st July. If that was the case then the C3 would be correct and you would have recourse to the installer as work was done to 16th but should have been 17th.
So if I go back to this company now, are they obliged to provide a satisfactory report, and if they refuse, do I have recourse to talk to the regulator that they are governed by? I think it’s NICEIC they told me

thanks

I assume that was the only C2 on the report? If so get back to them and inform them you have documentation that shows the Electrical installation work was started prior to the 1st July and that therefore it was correctly installed to BS7671 2001 (16th Edition) and therefore there was no requirement for all circuits to have RCD protection and see what they say.

Having said the above this company have inspected your property and it is their engineering judgement, The Regulations state that Installations completed to a previous edition of the wiring regulations may not necessarily be unsafe. However they may not change their view and still regard it a C2 (their judgment based on inspecting the property) and in that case you would either have the work done (can be by some one else as Littlespark said) or get another EICR done, a second opinion.

You currently seem to have NO RCD protection at all and I would strongly recommend you at least get some of the Circuits RCD protected. Especially an Electric Shower if there is one and the Socket Circuits.

Also as Littlespark said if this is rented out then I would personally advice you go with having the work done. One thing to take a view on a risk for yourself as opposed to tenants.

Personally if this is rented I wouldn't waste money on a 2nd EICR as that cost could go towards the remedials, shop around for prices and get the work done then it is sorted.
 
quite difficult to avoid rcd on all circuits these days ,all sockets, domestic lighting , bathroom or passing though bathroom, buried less than 50mm in a wall.
of course thats for new work, if renting out i would want that for my tenants
 
@PS Electrics there is no requirements for all circuits in a dwelling to have RCD protection.
No there isn't, I think the all in 5.12 on the EICR as stated by the OP "5.12.1, & 2, & 3), quote…“absence of 30mA RCD protection to all circuits excluding DB1" must mean that all circuits are affected by all the points covered in 5.12 Provision of additional protection by RCD not exceeding 30mA. Well that is how I understood it. So we have a lot of circuits concealed in walls less than 50mm probably.

Your request for the redacted EICR should hopefully shed more light on that.
 
Hi

Wiki (if it can be believed states "The 17th edition, released in January 2008 and amended in 2011 ("Amendment 1"), 2013 ("Amendment 2") and January 2015 ("Amendment 3") became effective for all installations designed after 1 July 2008."

It therefore stands to reason that this dwelling's installation was not designed and installed between 01-Jul and 08-Jul.

I think this inspector has got it wrong and it should be C3 and my choice as to whether i act on that.

Redacted Installation and condition reports attached if those help. Aware there are other C2's to be addressed, and have no issue with those

thank for the help
 

Attachments

  • Installation certificate 20080708 redacted.pdf
    1.9 MB · Views: 24
  • Condition report 20240725 redacteds short.pdf
    410.5 KB · Views: 28
It is irrelevant on what date the installation was completed, although it can be helpful to know.

An EICR is an assessment of the installation compared to the current edition of the regulations, and where there are non-compliances found, it is up to the inspector to determine whether each item should be given a classification code, and what code that should be (C1,C2,C3 etc).

Some inspectors seem to be a bit over zealous, some may be too blasé.
This is why there is commonly accepted industry guidance in the form of Best Practice Guide 4, made available as a free download from Electrical Safety First.

Even so, such guidance is just that - guidance.
The inspector on site must make his own judgement based on his own observations and experience.
 
It is irrelevant on what date the installation was completed, although it can be helpful to know.

Correct but there was an implication that it should have been installed to the 17th when it was installed to the 16th. If the C3 code related to something that should have been installed but wasn't the OP would have had redress to the original installer, if they are still in business that is. We only had the date of the EIC 10th July. It needed to be known that the installation was started before the 1st July 2008. Whilst it was very unlikely a Barn conversion could be done in 9 days one cannot assume anything.
An EICR is an assessment of the installation compared to the current edition of the regulations, and where there are non-compliances found, it is up to the inspector to determine whether each item should be given a classification code, and what code that should be (C1,C2,C3 etc).

Also there is the general guidance that Installations installed to an earlier edition of BS7671 are not necessarily unsafe.
 
I think this inspector has got it wrong and it should be C3 and my choice as to whether i act on that.

From the report it would seem the reason is that cables are concealed and buried to a depth of less than 50mm and do not have RCD protection, I am afraid that is a C2.

As littlespark said, by upgrading it solves a whole raft of potential problems that might be difficult to know for absolute certainty. Such as if a circuit runs through bathroom zone or not, if they do they require RCD protection. Cables installed to a depth of less than 50mm, not possible to know for absolute certainty that this isn't the case for every part of the circuit, if they do then RCD protection required. The possible use of portable equipment outdoors, not always obvious which sockets might actually be used, if all sockets are protected it removes this risk.

Interestingly if you watch the video by Eastway Electrical he installs an RCD socket outlet in a kitchen because of the requirement for RCD protection for portable equipment used outdoors, the socket outlet selected is the closest to the door but it is behind a fridge so not visible and could be missed. There are other socket outlets near windows and it is perfectly possible for someone to open the window and plug in the lawn mower that way for instance. If the whole circuit is protected then all possibilities are covered.
 

Reply to Has my UK property had its 10 year inspection performed correctly? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
509
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top