Boiler 9kw 50am breaker, ring 32a, ring 32a, oven 6.2kw 32a, heating 20a, lights 6a
This is then multiplied by 10 for the ten flats. Looking at diversity tables theres a strong possibility diversity cant be applied unless we could use column 2, heating & power - If not the cable size is going to be ridiculous as it needs to be in trunking, ratings go down etc.. What are peoples thoughts?

Why do you say there's a strong possibility diversity can't be applied? Over 10 dwellings diversity can definately be applied!
Your loadings seem very odd to me, it's almost as if you've counted the ratings of circuit breakers instead of actually calculating Ib.

If you've got a 9kW boiler why do you need another 20A circuit for heating?
 
I think you need a better electrical contractor.

Although diversity for a block of flats isn't exactly beginner stuff, the information you have provided (I presume has been provided by you by the contractor you've employed) is pretty duff.
 
Why do you say there's a strong possibility diversity can't be applied? Over 10 dwellings diversity can definately be applied!
Your loadings seem very odd to me, it's almost as if you've counted the ratings of circuit breakers instead of actually calculating Ib.

If you've got a 9kW boiler why do you need another 20A circuit for heating?
they are breaker ratings and the 20a for heating is just a radial going to a potterton economy 7 controller for controlling the boiler. I wondered if there was a diversity figure you could apply to there being 10 flats, its not something i have seen as yet though, thanks for the reply
 
I think you need a better electrical contractor.

Although diversity for a block of flats isn't exactly beginner stuff, the information you have provided (I presume has been provided by you by the contractor you've employed) is pretty duff.
According to you it is...
 
they are breaker ratings and the 20a for heating is just a radial going to a potterton economy 7 controller for controlling the boiler. I wondered if there was a diversity figure you could apply to there being 10 flats, its not something i have seen as yet though, thanks for the reply

Then you need to use the design current, not the mcb ratings, the reason for this is hopefully obvious.
This 20A heating circuit is a good example, it has a 20A mcb but the only thing connected to it is a timeswitch which will use a fraction of an amp. Over 10 flats that's 200A if you add up the mcb ratings, or maybe 2A if you add up the actual load.
 
Its ok, i have sorted it, thanks for mostly everyones helpful replies

Glad you got it sorted mate.
Next time it would be better to chat to an electrician and you can go through the design and what is needed together, rather than just bypassing them.
Every day a learning day...
 
Oven and hob for 6.8kw seems a bit light. Whilst modern ovens can just about run on a 13A plug (say 3kw), a typical 4 ring induction hob will be rated up to about 7kW.
 

Reply to the thread, titled "Have I got a big problem!?" which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top