So I’m fitting an electric underfloor heating mat by pro warm. I was testing it for continuity between L N and got 88ohms which is what it should be according to the instructions.

It says to do IR test at 500V but it doesn’t say between which colours. So I did L N and got 0.00ohms. Have I damaged the mat? I realised after maybe I shouldn’t have done that. I did L E and N E and it was >1049Mohms.

I looked at the instructions and it doesn’t say which cables to IR test between which was annoying.
 
You wont damage the mat by sending 500 or even 1000V from the megger down the live and neutral wires, the current from these meters is so low it wont do anything, I think its 1mA max.

On a similar note I've fitted loads of these mats over the years and tested each on before and after and never encountered any issue/fault anywhere. So I lay my own mat in my bathroom the other year and don't bother with the testing as its always been ok in the past, lay my own tiles very carefully and when I come to power up the mat for the first time - zilch. Must have been faulty from the factory, unbelievable.

Luckily I'm currently re modelling that bathroom and have just taken the floor up, this time I'll be a lot more through.
 
It says to do IR test at 500V but it doesn’t say between which colours.
I looked at the instructions and it doesn’t say which cables to IR test between which was annoying.

The instructions tell you to test the insulation and you already know from the result of the previous test that the L and N are not insulated from each other, they are connected together, so what further instruction is needed?
 

Reply to Have I possibly damaged the underfloor heating mat? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
586
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
821
  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
Replies
19
Views
2K
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
379
Is this a plumbing question or is your underfloor heating electric? It sounds like you have a mechanical problem, like a stuck solenoid /...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks