Top-Spark

Hi all, changed a db today and hay presto... Goodbye RCD!! :( been testing all day and still can't find the fault!! :( when I turn any light switch on the RCD trips but only if under load!! Remove the lamps, it doesn't trip!! :( both light circuits are currently on same RCD aswell!!
 
Onions, yes just downstairs.
Glen I have ramped it and it's >35mA at 0d and 180d?! Puzzling the hell out of me!! On paper there's nothing wrong?! Test results etc but RCD just won't have load!! :(
 
Time to strip the lighting down work out your route they take with resistance readings and bell out each cable to find your problem. It is there somewhere you just need to find it.

- - - Updated - - -

You said 0.78 earlier?
 
Ahh Glenn, now uv said that I haven't as gas and waters joined 2 main earth In meter box!! Habit of just disconnecting the main earth at db hay!! U lot r ace... Knew I'd overlook something simple!! Ill get proper result 1st thing!! :) cheers
 
Ahh Glenn, now uv said that I haven't as gas and waters joined 2 main earth In meter box!! Habit of just disconnecting the main earth at db hay!! U lot r ace... Knew I'd overlook something simple!! Ill get proper result 1st thing!! :) cheers
yes..
always remember that just dropping out the main earthing at the dis-boards earth bar is not a guarentee of eliminating parrallel paths...
always look for earth blocks/earth marshalling points...

- - - Updated - - -

Ahh Glenn, now uv said that I haven't as gas and waters joined 2 main earth In meter box!! Habit of just disconnecting the main earth at db hay!! U lot r ace... Knew I'd overlook something simple!! Ill get proper result 1st thing!! :) cheers

good lad..
 

Reply to head banging... help needed!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
492
davesparks
D
Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2
Replies
42
Views
2K
  • Question
It's ok if you use the correct driver for the application.
Replies
14
Views
2K
loz2754
L
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
857
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks