this is baffling.
situation is an existing rfc that has had a minor repair. a socket had been removed and the live cables left in back box and tiled over. cables were pulled back above ceiling and jointed.

prior to reconnectio in a new CU tests were done on the circuit.

now here's the baffling bit:

r1 = 0.28
rN =0.28
r2 = 0.47

fine so far, expected R1+R2 = (0.28 + 0.47) /4 = 0.1875

measured R1+R2 = 0.17 . perfeck.

then, here's the rub....

Rn + R2 = open circuit, tested at 2 points on the ring.

both R1 + R2 and Rn + R2 measured with the respective ends cross connected @ CU.

it's as if the N's are continuous but loose in the sockets but sockets were working fine before.

tester plug lead checked as OK by plugging in a socket on another circuit and live readings were normal.

as i said, a head scratcher.
 
this is baffling.
situation is an existing rfc that has had a minor repair. a socket had been removed and the live cables left in back box and tiled over. cables were pulled back above ceiling and jointed.

prior to reconnectio in a new CU tests were done on the circuit.

now here's the baffling bit:

r1 = 0.28
rN =0.28
r2 = 0.47

fine so far, expected R1+R2 = (0.28 + 0.47) /4 = 0.1875

measured R1+R2 = 0.17 . perfeck.

then, here's the rub....

Rn + R2 = open circuit, tested at 2 points on the ring.

both R1 + R2 and Rn + R2 measured with the respective ends cross connected @ CU.

it's as if the N's are continuous but loose in the sockets but sockets were working fine before.

tester plug lead checked as OK by plugging in a socket on another circuit and live readings were normal.

as i said, a head scratcher.
Can you get access to the joint you mentioned?
 
You only have to have neutrals twisted together and then put loosely in the terminal for the connection to be somewhat variable, I would usually expect high resistance rather than open circuit though, especially as the sockets were working.
However any small movement of cables such as when they were brought out of the wall may have affected nearby sockets.
 
You only have to have neutrals twisted together and then put loosely in the terminal for the connection to be somewhat variable, I would usually expect high resistance rather than open circuit though, especially as the sockets were working.
However any small movement of cables such as when they were brought out of the wall may have affected nearby sockets.
thought of that, so just for a laugh, tried Rn+R2 with a 500V IR test. came back with 500Meg.
 
this was a problem that another member had me look at. time was limited as it was 4.00pm yesterday and after sorting out the fault on another job ( see new Ring circuit tripping RCD thread), was gasping for a beer and 25 miles back home.
 
Can you get access to the joint you mentioned?
can do pete, but that's the next thing for Simon to check. i was only there to give him a second opinion and some pointersas to how to proceed. end of the day, we don't usually test N-E continuity. it's just someting he picked up on when trying to get his head round testing.
 
that's what i have told Simon to do. seems like the N connection is not being seen by plug in . strange though it's same at original (1980's ) sockets and also at new added ones.
 
Either the customer went round unscrewing sockets whilst the CU was being put in place or the cables have been mixed up and you are measuring the neutrals with the cpc of another circuit.
no customer. flat is empty, undergoing refurb. apart from the o/c Rn+R2. all other dead tests are perfect.
 
You wanna be careful Tel, some members might suggest (not me) that your out of your depth, and should get someone in who knows what they're doing :)

I just say that 'cos it just shows, none of us are connoisseurs of the lecky art, and how useful this forum is.
 

Reply to Head Scratcher Time. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top