hi all i have recently done an new installation on a garage a very very large double garage to be more precise anyways my question is this i had to install two heat alarms,1 alarm for each car bay if you catch my drift.
my question is this, does the same building regulation apply to the installation of heat alarms in 17th ed boards or does it change i assume its the same but i would like to have a definitive answer. ta
The "building regs" would apply in terms of the age of the building - so if it is a new build, then yes, it will require fire prevention measures to be implemented. Whether that runs to the need to install automatic fire detection at all, depends upon the scope and nature of the building, proximity to living quarters, construction, storage of flammable materials etc.
Should there be a need for automatic detection, it will likely be required to comply with BS 5839-6 at some level or another, in which case, it may very well also require interlinking with detection in the living area of the property too. A Fire Risk Assessment would identify the need, and level of detection required.
As for technical aspects, assuming automatic detection is required, then heat detection should NOT be installed as the sole means of fire detection. Combined detection is available, which can detect both heat and smoke, or if not, in the range of equipment in use, a smoke detector should be fitted in an appropriate area, or detectors in areas, as required, in addition to heat detection.
As to whether interlinking of the detection is required, this depends on the Grade of fire detection required.
However, a very, very large double garage, on its own, isn't the most descriptive of terms, in relation to why you say you had to fit them - why? Is it part of, or close to, living quarters? Or is it an insurance requirement due to the value of property within the garage?
Part of why I ask - it's going to be fairly pointless fitting any detection at all, if it is remote from a living area, and nobody can hear any sounders fitted.....you may as well just wait until the owner sees the flames.
If you can offer a bit more info as to why they were required, and the nature/location of the garage, I can provide a more definite answer for you.
As regards electrical connection, all that's really required for mains fed detectors is that they be connected via a non-RCD protected MCB, preferably dedicated to the detectors.