Anything fire alarm should be fed from its own MCB wherever possible, for precisely the reason you mention, and the reason you give for "not".
If a lighting circuit goes, the back up batteries, often only alkaline, in a smoke alarm will be called into play. Once an alkaline battery is called into play, it will lose its charge fairly quickly. This in turn, may cause the detector NOT to operate when needed.
Besides --- If a lighting circuit trips, you can always tell......the lights don't work!
If a smoke detector circuit trips and the detectors aren't letting you know audibly there is no mains feed - CHANGE THEM NOW.
As for preferred methods, it is a BS5839 - 1 and 6 requirement that the supply is taken from an independent source. IMHO it should apply to ALL classes and categories of system. They should never be put on an RCD/RCBO protected circuit either.
It is NOT good practice to wire smoke detection into lighting circuits at all, frankly. If fire detection must share a source with lighting, then it should be at the MCB and nowhere else.
I am also of the humble opinion that ALL mains fed smoke or fire detection should be interconnected using fire resistant cable - most certainly where interlink functionality between one detector and another is required (unless wireless, obviously).
Guidance given by the IEE and a manufacturer, differs a little from your sensible approach to fire alarm supplies
Your opinion (which differs from Bs 5839-6) quote
It is NOT good practice to wire smoke detection into lighting circuits at all, frankly.
The prefered method of the IEE as in the on-site guide where all circuits are protected by rcds,"there is advantage to wire them off a regularly used local lighting circuit "
On site guide page 66 Note
We, as always, need to take care to be clear what is personal preference,so that the choices remain clear on these muddy issues
Another point which was used to assist the view of a seperate supply for these type of alarms was
quote
If a lighting circuit goes, the back up batteries, often only alkaline, in a smoke alarm will be called into play. Once an alkaline battery is called into play, it will lose its charge fairly quickly. This in turn, may cause the detector NOT to operate when needed.
This is the advise taken off the aico site in this regard
Battery life expectancy
quote
This will depend on a number of factors that will differ slightly
according to the type of alarm in use.
The 140 series alarms are supplied with an Alkaline battery which,
dependent on conditions, can provide up to 4 years standby supply,
up to 2 years without mains power.
The 150 series and the 160 series alarms are fitted with rechargeable
Lithium power cells which are continuously charged by the alarm
circuitry. They have a life expectancy greater than that of the Smoke
Alarm, i.e 10 years or more,which eliminates the need for
replacement.
That advise appears to contradict one of your personal reasons why a local lighting circuit should not be used
I make these comments as an electrican who has limited skills in alarm systems and installation
The comments I have made are based on guidances given to us where doubt may exist
I welcome your comments on the points made above
Regards Des
Thanks very much Bill
That was a very interesting read and I do appreciate that experience and knowlege sometimes well outwiegh standard advise given by the "Rulemakers"
The points you made are driven by first hand experience and I will certainly take on board those views
Most on this forum who are involved in other sectors have little choice,other than to trawl the guidances, and take whats in them as the best information to be followed
As an electrician I sometimes cringe at opinions of new starters etc who blindly follow and dot every I and cross every T with total adhesion to what may be in appropriate working practices etc
Sometimes whats in a book reflects little on whats found in the real world,so in that sense I feel in the position of the new starter and will have an open mind on the questions
Its good know that we have experience and knowlege like yours available on this forum