A neighbours underfloor bathroom heating mat stopped working a while back, she asked me to look at it today. Turns out when it was installed the joiner had accidentally burst the cable for it. It's a small thin blue cable that heats up that has two conductors & an earth. Someone has done a repair on it underneath floor which looks like they have used proper kit, crimps, heat shrink etc. I've just took a voltage reading at the programmer which is fine going in & out & Ive peeled off the heat shrink & took a reading between each of the conductors & earth & on one I'm getting 150v & the other I'm getting 90v. Any ideas? Mat just needing replaced I'm guessing.
 
Ok. Update, she doesn't seem to think it's working correctly as there's one area where a tile is cold, then one where a tile is a lot warmer than the rest. I redid all the tests today, resistance between the two conductors is as it should be, around the 58 ohms mark, I done an IR again live to earth >299, neutral >299. Reading at the programmer is still the same, 230v leaving programmer but still voltage between both conductors & earth at the join. A friend who is also an electrician looked at it today & he thinks it's ok, possibly something to do with the type of mat or the actual cable/wires that heat up but I'm not so sure. It's like the voltage (240ish) is split exactly over the two conductors, judging by readings at join. I also bypassed the programmer & results are still the same.
 
well if your readings are correct & the programmer is working, check the Resistance of the sensor with multi meter just to make sure.
next thing get the mat up hot for couple of hours & use IR camera then should be able to trace the heat pattern around the floor, this should show if any of the heat mat has been laid under the cold spot or not, same with the hot spot might have been the spare if any & have a more dense area of the heat mat in that area.
IR camera will tell you also you can check the joint same time.
 
Ever heard of volt drop across a resistor?

You think this is why I'm getting those readings?

Do you know how the mat is laid out ?
And how its's wired.
Is it just one continues run ?
Or are there several area's all coming together somewhere ?

Spoke to joiner today, says it's one big continuous run, one mat. It's only an area of 6m squared. He says hotter & colder tiles are common due to density of tile adhesive.

well if your readings are correct & the programmer is working, check the Resistance of the sensor with multi meter just to make sure.
next thing get the mat up hot for couple of hours & use IR camera then should be able to trace the heat pattern around the floor, this should show if any of the heat mat has been laid under the cold spot or not, same with the hot spot might have been the spare if any & have a more dense area of the heat mat in that area.
IR camera will tell you also you can check the joint same time.

Can I ask why I've to test the sensor? Afraid I've not got an IR camera. Thanks for the suggestion though, would have been ideal.
 
sensor will feed back to the unit to turn floor on & off, if sensor is faulty could cause mat to turn on or off at random, normally test it during set up.
IR camera think you can hire them only need the hand held unit
 

Reply to Heat mat fault, neutral earth reading... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top