Hi fellas

I've got an outdoor heating circuit that I'm trying to fault find.

There are four heaters under a parasol each rated at 1.5kW that are tripping two MCBs in series. One is on the main board the other is in a separate unit dedicated to the outdoor circuit. When the heaters are cold if all four heaters are plugged in then both Mcbs trip instantly. If only two are plugged in it starts and then you can plug the other two in and there's no problem. Then when it times out if it's switched back on immediately then they come on without a problem.

Both MCBs are B types BSEN 60898 hager and MK.
There is no problem with IR
The measured resistance of a heater when cold is 4 ohms
This would give each one a starting current of 57.5 A
So the four together would have a startup current of 230 A or 52 kW

My first thought was to change the MCBs to C or D types but on reflection of these figures that would just result in a tripped main switch. I am thinking of some sort of soft start current control option but I haven't used one before and I'm not sure if that's the best solution.

Apparently it used to work, but I don't see how.

All thoughts welcome.
 
No they don't have 13 A plugs, they have small connectors about 20mm wide with 2 rounded pins and a flat earth strip along one edge. I don't know what they're called and they have no internal fuses.
 
Apology accepted, but out of the 10,000 or so appliances I've PAT tested I've never come across a connector that's exactly like this. So it's rare but my god boys PM me your addresses and I'll send you some pills seems like you need them .
 

Reply to Heater start up currents in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K
I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
378

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top