Go Wales Go. seriously, I have a separate ring main 2.5 cable on a 32 mcb. It has 7 1kw heaters connected. Does this sound okay. The electrician has signed it off ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss heaters in the UK Electrical Forum area at ElectriciansForums.net
Regulations recommend not too
Do they? Which regulation would that be then?
Go Wales Go. seriously, I have a separate ring main 2.5 cable on a 32 mcb. It has 7 1kw heaters connected. Does this sound okay. The electrician has signed it off ?
Appendix 16 note ii " not supplying immersion heaters, comprehensive electric space heating ​or similar"
Granted it is not a regulation, but it is guidance on the use of reg 433.1That is not a regulation, and it is also concerned with a ring final serving socket outlets. The OP is talking about a ring which has been designed and installed specifically to serve heating points.
Granted it is not a regulation, but it is guidance on the use of reg 433.1
It is concerned with RFCs using socket outlets and FCUs which I assume is being used here
But surely the heaters will be connected via BS1363 FCUs making it a RFC as per 433.1.204I read the OP as if the circuit is exclusively for the 1Kw panel heaters, so it doesn't apply IMHO
I think I would of preferred two 20A radial circuits
Granted it is not a regulation, but it is guidance on the use of reg 433.1
It is concerned with RFCs using socket outlets and FCUs which I assume is being used here