Hi there
To start with, I am not an electrician but I hope that you are willing to help?, I am currently fitting out a shell of a room, i.e battens, insulation, sockets, plasterboard etc. Before I insulate I need to lay the electric cables for both sockets and lights, the room has not had electricity in it previously (just laying the cables, I will be getting an electrician in to do the actual connecting), the sockets are simple and I understand but I am unsure as to which method I should cable the lights, as I understand it can be either Loop at Light or Loop at Switch, are there any benefits to either or do the regs now require a particular method?
Hope you can help?
Peter s
 
Hi Peter, welcome to the forum. In answer to your question, 'Loop' at the light or switch will really depend on what sort of luminaires you intend to install or the nature of the installation.

I note you are not an electrician, but intend to install the cables, and get an electrician in to connect. If you asked me to do this, as an electrician I would decline. Being responsible for the final connection, I would be taking on some of the responsibility of the correct installation of the cabling.

Before circuits are energised, they need inspection & testing, using appropriate test equipment.

I would suggest you rethink your project, and employ the services of a competent electrician.
 
Hi Peter, lots of things to take into account:
How are you intending to feed the lights and sockets?
You need to understand that running cable in insulation may need some sizing calculations.
What type and size of cable are you intending to use?
Lastly I doubt very much if any decent Electrician would undertake connection, testing and certification of an installation he/she has not actually designed and installed, sorry to sound so negative, but you admitted you are not an Electrician, your best bet would be to employ one from the outset of your project, you could watch and learn from the experience.
 
Get hold of a local sparky ( use the right channels and not a mate of a mate down the pub).
Tell him/ her what you are proposing and want to do the first fix yourself to save time and coin.

They will charge you, but will tell you what you need to do and he/ she will need you to call them back to check progress before you cover it all up in nice new Plasterboard.
Then he/she will come back and test/ make off all termination and do the final test.
Don't just chuck cables in as you may find most sparkles will walk away or get you to re do the cable runs.

Good luck
 
Thanks for getting back so promptly guys and I completely understand about an electrician wanting to be involved throughout and will involve one before I plasterboard so that they can see exactly how I have routed the cables. I have used a simple radial circuit for the 4 double sockets 2.5mm cable, the insulation is rockwool not Celotex, the lighting (1.5mm) will be 2 lights off a 2 gang switch (1 fluorescent 1 standard) and 2 lights (standard) off a 1 gang switch, the room is in a barn and I intend to have a separate CU in the barn for this (other rooms to be added when I can afford to do the work). National grid have upgraded our house supply from 60 amp to 100 amp so there is adequate supply.
Throwing out a question like this with you guys not having any background of the 'bigger picture' will understandably cause you to be reluctant to give info, perhaps I should have just asked what the difference between LTL and LTS was and which one is most commonly used now?, I am not trying to circumvent the system I just have to keep costs down or the project won't happen but it has to for reasons which I don't want to go into.
Anyway I hope someone will be able to help?
Many thanks
Peter S
 
Are you using any form of mechanical protection for the cable runs?
I'd also suggest you get a local sparky involved so he/ she can go over your intended routes. It sounds simple but the method of installation is the biggest factor on what cable sizes to use.
It could be your barn is only 10m sq, but it could also be 100m sq.
Get someone in as mistakes at first fix can cost a few hundred to fix at the final stage.
 
... they can see exactly how I have routed the cables. I have used a simple radial circuit for the 4 double sockets 2.5mm cable, the insulation is rockwool ... Peter S
Hi Peter,
The installation method is very important here. Using Method 103 the 2.5mm is rated for only 13.5A - no good at all. A small change to Method 102 and its 21.5A. But you can't do that afterwards, which is why on-site advice from the Electrician is so important ...
 
I intend to have a separate CU in the barn for this (other rooms to be added when I can afford to do the work). National grid have upgraded our house supply from 60 amp to 100 amp so there is adequate supply.

Now you are talking about adding a separate CU - you should really get a local spark involved..... then there is planning and Part P.....
 

Reply to Hello and project question? in the The Welcome Forum area at ElectriciansForums.net

Similar threads

Thanks for the warm welcome Dave! Didn’t fancy counting the gas route then?
    • Like
Replies
2
Views
287
Welcome to Electricians Forums :) Thanks for signing up. :D
Replies
2
Views
335

Search Electricans Forums by Tags

Tags Cloud - Most Used Words - Use them to search for topics

110v 12v 17th 17th edition 18th 18th edition 2 way 2330 2365 2391 240v 3 phase 6mm access account across adding additional advice advise after again alarm alarms always am2 amendment amp another answer anybody anyone anything appliance appliances application apply apprentice apprenticeship approved area arial armoured around assesment assessment attach aus ausie elec available basic bathroom batteries battery because become becoming becsa before being bell best better between black block blowing board boards boiler bonding book books bosch box boxes brand breaker breakers british bs7671 bsi build builder building bulb bulbs business button c&g cable cable size cables calculation calibration camera can't canada car caravan card career cctv ceiling central central heating cert certificate certificates certification certs certsure change changes changing charge charger charging cheap check cheers christmas circuit circuits clamp class code codes college combi coming commercial companies company competent complete condition conductor conductors conduit confused connect connected connecting connection connections connector connectors consumer consumer unit contact contactor content continuity contract contractor control controller conversion cooker copper core correct cost council couple course courses cover cpc cps crabtree cupboard current customer customers dead deal degrees demand design details detector device dewalt diagram difference different dimmer dimmer switch dimmers distribution diversity diy dno doing domestic domestic installer don't door double downlight downlighters downlights drill driver earth earth rod earthing east economy economy 7 ecs edition eic eicr elecsa electric electrical electrical installation electrical nvq electrical tools electrical wiring electrical work electrician electricians electricians london electricians mate electricians vans electricity electrics electriians mnchester element email emergency emergency lighting employed energy engineer engineering enough entry equipment essex every everyone exam existing experience extending extension external extra extractor extractor fan fan fans fault fault finding faulty fcu final finding fire fire alarm first fit fitted fitting fittings fixed flat flats flex flickering floor fluke fluorescent for sale forms forums found free fuse fused fused spur fuses garage garden gas generator get getting going great green grid ground gu10 guidance guide guilds hager halogen happy having heat heater heaters heating hello help help please help! hi everyone hnc hob home honeywell hot tub hours house how to ideas immersion impedance improver in london incoming induction industrial industry information infraction inside inspection inspection and testing install installation installations installed installer installers installing insulated insulation insulation resistance insurance interesting intro introduction inverter inverters isolation isolator issue issues jib jib card job jobs joining junction keeps kewtech kit kitchen knowledge lamp lamps large lead leads leakage led length lenny level level 2 level 3 light light switch lighting lighting circuit lights little live load local location loft london long looking looking for work loop low voltage ltd machine main main switch mains maintenance makita manchester manual mate max maximum mcb mcbs mcs media megger member members message metal meter meter tails meters method metrel mft might minor missing mobile module money motor mounted mounting moving multi multifunction multiple murdoch myself napit need help needed needs neutral never new new build new member newbie niceic night no earth north not uk not working notifiable number nvq off offer office old online opinions options other out outbuilding outdoor outlet outlets output outside oven overload panel panels parallel part part p passed pat pat testing people periodic person pfc phase phone pipe pir place plan plastic plate please plug plumbing advice pme point points pole position possible post posts power practical practice price prices pricing private problem problems project property protected protection protective pump pvc qualification qualifications qualified quality query question questions quick quote radial range rated rates rating rcbo rcbo's rcbos rcd rcd tripping rcd's rcds reading readings really recommend recommendations red regarding registered regs regulations relay remote repair replace replacement replacing required requirements resistance results rewire right ring ring final ring main roman roof room rose running safe safety salary sale saying scheme scotland screwfix sds second section security self self employed sensor series service services shed shock short shower simple single single phase site plan size sizing skills sky small smart smoke smoke alarms socket sockets software solar solar panel solar pv someone something sorry source south spark sparks sparky split spur spurs standard start starter starting steel still storage storage heater strange strip students stuff sub main suggestions supplier suppliers supplies supply supply to surge swa switch switched switches switching system systems t&e table tails taking terminal termostat test tested tester testers testing tests thank the forum their thermal thermostat these thing things thinking those though thought thoughts thread three three phase through time timer times tips today too tool tools trade trainee training transformer transformers trip tripped tripping trips trunking trying tt system type under underfloor underfloor heating unit units update upgrade urgent used using value values valve van vehicle video volt drop voltage voltage drop volts wall wanted warning water weeks welcome west what's whats where white wind wire wired wireless wires wiring wiring help within without work working works worth wrong wylex years zone zones

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top