Huw Jenkins

Firstly, I've decided to put my head above the parapet and say hello to everyone here, also looking for some advice regarding a re-wire of a 2 bed bungalow I'm about to embark on.

My client has instructed me to carry out a full re-wire of his 2 bed bungalow, now I know regulations say on a re-wire you can replace like for like, however, he's having it done for the purpose of possible sale, so my question is; the current CU is located above a fixed wardrobe in bedroom 1 of the property, when installing the new cu, should I place it where the previous on is, or should I move it to apply to the 450-1200mm recommendation
 
Accessibility to a consumer unit is a good idea, however there is no requirement to move it when changing it on an existing installation.
This would be a discussion between you and the customer on what they are prepared to have done.

Welcome to posting.:fearful::door::gun::blush:
 
as richards'spost.no need tomove it unlesss at customer's request. and it's not 450mm - 1200mm for a CU. more like 1400mm -1500mm , but that's only on new builds.
 
On a rewire you can put the accessories and cu at heights agreed with the client...... Personally the new build height is a bit silly unless it's in a cupboard .....

And don't forget to recommend mains smokes ...... They aren't required on our regs but a very sensible addition ...
 
Thanks guys, think it's best left where it is then, my quote given to him includes the main smokes, as I think it's good practice to install these as standard on re-wires, and the current installation leaves a lot to be desired, that's what happens when you deal with a house with 30 years DIY work done
 
Personally, as its a rewire, I'd put it somewhere more sensible than above a wardrobe :)
Probably depends on the cost of the DNO moving the supply and how much the customer is willing to pay, I agree with you're post though.:carpstreamer:
 
Last edited:
Yeah above wardrobe is not the best place, however the DNO costs would have to be factored in, and plus he's having the re-wire in order to place bungalow on the market, so maybe make sure my company sticker is on the new CU so the next occupant can call me to move it
 
Yeah above wardrobe is not the best place, however the DNO costs would have to be factored in, and plus he's having the re-wire in order to place bungalow on the market, so maybe make sure my company sticker is on the new CU so the next occupant can call me to move it
That seems almost cavalier Huw, do a rewire put the CU where it was originally and hope the new occupant wants it moved. What are you going to do leave loads of spare cable in the roof space just in case?
 
Yeah above wardrobe is not the best place, however the DNO costs would have to be factored in, and plus he's having the re-wire in order to place bungalow on the market, so maybe make sure my company sticker is on the new CU so the next occupant can call me to move it

The service head can stay where ever it is, doesn't stop you moving the location of the CU.
 
The service head can stay where ever it is, doesn't stop you moving the location of the CU.
Agree, but it would be nice to move it after the customer had gone to the trouble of having a rewire, but may be thats me just being an old git
 

Reply to Hello from me, and opinion welcom in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top