My first post on my first job...
I have just installed an extractor fan. It was going to have a timer but the house wiring is confused: the switch and light are not connected directly, instead the cables go off under the floor boards and yet the switch is 50cm from the switch??
So the light and socket both have blue tape around the neutral wire indicating switch lives? My guess is there must be a junction box somewhere?
All of the test values were fine, until I opened the isolater switch. The value was below the 1 meg minimum, and a similar value from the extractor when switched off at the isolater. When switched on and working I get 0.48 ohms.
Should the extractor be connected to the pull cord instead of the ceiling rose, which only has a line and switchline.
Is it possible the isolater has a fault? It is a schlumberg which I thought reliable. Any and all help gratefully received
My first post on my first job...
I have just installed an extractor fan. It was going to have a timer but the house wiring is confused: the switch and light are not connected directly, instead the cables go off under the floor boards and yet the switch is 50cm from the switch??
So the light and socket both have blue tape around the neutral wire indicating switch lives? My guess is there must be a junction box somewhere?
All of the test values were fine, until I opened the isolater switch. The value was below the 1 meg minimum, and a similar value from the extractor when switched off at the isolater. When switched on and working I get 0.48 ohms.
Should the extractor be connected to the pull cord instead of the ceiling rose, which only has a line and switchline.
Is it possible the isolater has a fault? It is a schlumberg which I thought reliable. Any and all help gratefully received