pdab09

DIY
Joined
Nov 20, 2020
Messages
8
Reaction score
0
Location
Wales
As an old time City & Guilds electrician who last worked as such back in the1960s I realise I’m a bit stone-age to say the very least. That said my daughter just installed a decent shed in the garden of her new home and rather conveniently there is an un-made SWA cable laid from the house distribution board to the shed and I’ve been asked to get it all up and running for her. From her pictures of the loose cable I think it’s 2 core 4mm SWA but I’ve not seen it as she lives a considerable distance away (this will be a long weekend trip / job). Now I intend to install a small, metal consumer unit with an RCD, two lights and a 2-gang 13A socket outlet on MCBs. I’ll most likely use plastic conduit and metal clad fittings. Where I’m a little uncertain is where I pick up the mains feed from the house. My daughter can’t see the SWA cable and I’m guessing it tucked away in the house distribution unit. Never used a RCBO but I was thinking of an RCBO and a DIN rail, double pole isolator switch. Also, believe the household distribution unit comes under Part P – is that correct. Any pointers / advice appreciated.
 
As an old time City & Guilds electrician who last worked as such back in the1960s I realise I’m a bit stone-age to say the very least. That said my daughter just installed a decent shed in the garden of her new home and rather conveniently there is an un-made SWA cable laid from the house distribution board to the shed and I’ve been asked to get it all up and running for her. From her pictures of the loose cable I think it’s 2 core 4mm SWA but I’ve not seen it as she lives a considerable distance away (this will be a long weekend trip / job). Now I intend to install a small, metal consumer unit with an RCD, two lights and a 2-gang 13A socket outlet on MCBs. I’ll most likely use plastic conduit and metal clad fittings. Where I’m a little uncertain is where I pick up the mains feed from the house. My daughter can’t see the SWA cable and I’m guessing it tucked away in the house distribution unit. Never used a RCBO but I was thinking of an RCBO and a DIN rail, double pole isolator switch. Also, believe the household distribution unit comes under Part P – is that correct. Any pointers / advice appreciated.

You will need to fully test the cable prior to anything, if it's OK, don't use a RCBO use a MCB in the cu if you can.

If not, you need to split the tails and take it into a kmf and feed the shed from that.

Personally I would use RCBOs rather than a RCD and MCBs in the shed.

The only reason to use a RCBO at the consumer unit is if the Zs is too high for the MCB and you need the RCD aspect for fault protection. (In that case you would need to have a kmf first, then an RCD - if you can't get the RCBO in the cu)

Given the load, and cable size (4mm) you should be able to select a MCB rating to suit the load and Zs.

If it's in England/Wales yes it comes under part P.
 
If it's 2core then that means using the wire armour for earth - or you TT the shed, or you need to run a separate earth.
Assuming disconnect times can be met, it doesn't need RCD protection - meaning MCB at source end and RCD can be fitted at load (sged) end where it's more convenient to reset. For discrimination, consider a fuse. Or, you might just omit fuse/MCB for socket (use RCD socket) in shed and just fuse down the lights (could use a switched FCU.)

"Part P" is irrelevant ! What matters is wgether the work is notifiable. If you are lucky then it might be possible to not create a new circuit - e.g. there might be a circuit you could "modify". If that's not the case, e.g. you need to add an MCB, then you either need to notify the local authority building control (LABC) dept. before starting work, or you need to defer the work to someone who can register via their scam.
 
If it's 2core then that means using the wire armour for earth - or you TT the shed, or you need to run a separate earth.
Assuming disconnect times can be met, it doesn't need RCD protection - meaning MCB at source end and RCD can be fitted at load (sged) end where it's more convenient to reset. For discrimination, consider a fuse. Or, you might just omit fuse/MCB for socket (use RCD socket) in shed and just fuse down the lights (could use a switched FCU.)

"Part P" is irrelevant ! What matters is wgether the work is notifiable. If you are lucky then it might be possible to not create a new circuit - e.g. there might be a circuit you could "modify". If that's not the case, e.g. you need to add an MCB, then you either need to notify the local authority building control (LABC) dept. before starting work, or you need to defer the work to someone who can register via their scam.
You can utilise the armour as the cpc.
 
Yep - just found out it's an aluminium panel shed! Guess that'll have to be bonded?
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have sufficient cross section for ECP bonding.)

Just being metal doesn't necessarily mean that it could introduce a potential from outside, it could merely be a piece of metal (we don't bond cutlery for example), although likely to be a Exposed conductive part, so may require bonding, but not needing such a large conductor cross section.
 

Reply to Help / Advice required in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
712
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top