Domestic property
Supply number 1
6 flood lights 4x400watt= 1600 watts
250meters from board to closets corner of tennis courts
Tennis court size
23m x 10m
My calculations are suggesting a
16mmsq cable
2.4% volt drop
Would anyone have any advice for doing long distances in a garden?
Supply number 2
Driveway 150meters
Cable length 200meters from fuseboard to 15 bollards lights (15x5w)=75watts
calculations
230v
75 load
1.5mmsq cable
Volt drop 0.8%
Many thanks
Supply number 1
6 flood lights 4x400watt= 1600 watts
250meters from board to closets corner of tennis courts
Tennis court size
23m x 10m
My calculations are suggesting a
16mmsq cable
2.4% volt drop
Would anyone have any advice for doing long distances in a garden?
- 10-16mm to a halfway point and distribute out for both circuits
- apply diversity?
Supply number 2
Driveway 150meters
Cable length 200meters from fuseboard to 15 bollards lights (15x5w)=75watts
calculations
230v
75 load
1.5mmsq cable
Volt drop 0.8%
Many thanks