I have a design unit and 14 circuits to do. Can some one please help as I have completed 1 of my knowledge and before I crack on any help on this would be great. It's a rough copy so excuse the mess. Thanks. It's question 4. Thanks
[ElectriciansForums.net] Help cable calculation please newbe
[ElectriciansForums.net] Help cable calculation please newbe
[ElectriciansForums.net] Help cable calculation please newbe
 
Sorry I am out of time at the moment, but on a quick look the actual Ze at the origin of the installation is 0.09 Ω.
Then there is a supply to your distribution board and at that board the Zdb is 0.11 Ω, note this is different from 1.01 Ω.

For your calculation use the value 0.11 Ω as the additional resistance from the non final circuit part of the fault path, equivalent to Ze for your calculations.

On a quick view the numbers look right for your first post about circuit two but disconnection times are on p.55 not p.58.

On the redone one you have the calculation for volt drop wrong.
The answer you get (6.2V) is for a mV/A/m value of 19, which would be 2.5mm² cable.
You have written the calculation using 31 which is the value for 1.5mm² cable. This makes all the following calculations wrong because the cable size is incorrect.
 

Reply to Help cable calculation please newbe in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
To be honest James I use an app- Electrical Calculations. It auto calculates the cable size once you enter the specifics/parameters. Voltage...
Replies
5
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top