Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss help calculate cable size for 130kw in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hope you didnt take my post wrong but il check later as im on my way out but at first viewing check your connecting to equipment rated at 90degrees if your using those tabled values or better still refer to 70 degree SWA (4D4A) and if you calc for a cable is correct the addition of both cables needs to be over Iz not each cable .... you have just run 2 x 185mm cables giving you a total value of 486amps Table 4D4A
Table 4D4A .... 70mm = 143amp ref method D so 2 x 143 will meet your Iz all you need to do then is check your volts drop complies.
no problem. thanks for the reply. the data sheet in the photo above is for one air con unit. there will be two units fitted. therefore there will be two 4 core swa cables.
What are you air conditioning ????? ..... London!!
If you can run 2 seperate parallel cable run 1m apart then you can benefit from large savings on cable sizing.... so as above then another run the same 1m apart, or as johnboy said account for both to a submains and split at load end, although the diversity may not be a candidate to reduce size as in hot weather both units could be expected to be at full load for long durations so wouldn't in this case go down that route.