iQ electrical i understand were your coming from there are easy methods im just talking about a particular job we were doing on raft lighting in a office area that was the method we used the conuctors were the same cross sectional area ie 1.5mm so if the r2 was 1 ohm r1 would be 0.50 ohms so we then calulated the zs on are engineers instructions long winded i know but there you go
I think I'm losing the will to live, if the conductors were the same csa, why would you have different values?
You should ask your 'engineer' to show you where this procedure is documented in Guidance Note 3.
I'm not 'having a go' at you but it's important to show the correct procedures on the forum as many use these threads for answers and as study aids for 2391-10 etc.