a few questions can anyone please help.

on the second page particulars of installation at the origin, it states number of smoke alarms do you fill this in if you have fitted the smoke alarms yourself or do you still fill it in i.e put down 2 even if their is 2 smoke alarms in the house.

under main switch or circuit-breaker if it is a sub main do you put the main switch in this case a 61009 rcd or the mcb 60898 type 2 feeding the board.

is the max zs permited for a 60898 type 2 the same as a type b.

insulation resistance testing line/line what is this live to live on a ring main only.

:confused:
 
Only the work you cover! If you install a single circuit then NO, if you do a board change then YES!

Main Switch will be the 61008 Rcd on a sub board.

60898 type 2 ?? Do you mean 3871 type 2 ? If so then NO!

IR Line/Line, I thought that was for 3 Phase only...!?

Cheers
 
Last edited:
1) I have never seen smoke alarms detailed under the particulars of the installation ? What is the design of your cert?
2)Main switch or circuit breaker refers to the main switch or circuit breaker for the INSTALLATION not the submain. IE main switch on incoming consumer unit so 61008 by the sounds of it
3)type 2 ? sounds like a BS3871 MCB you have there not a BS60898
4)I R line to line refers to three phase only not applicable for ring circuits


Spud
 
5 s if cabling run surface and supply outlet rated greater than 32A. (which i assume it is if 40A) is it a shower or cooker? only 0.4 s if cabling behind plaster or in partition @ depth less than 50mm
 

Reply to help compleating domestic electrical installation certificates in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Solved
An NVQ is a vocational qualification and is based upon your work experience and what you put into your portfolio for your assessor to judge you...
Replies
4
Views
715
  • Question
I’ve been told I will need to show current working on 3 phase distribution board, metal tray, metal trunking, metal conduit, PVC tray, PVC...
Replies
1
Views
2K
  • Question
https://www.hiscox.co.uk/business-insurance/bi?traffic=PPC_Brand&cmp=Brand&&infinity=ict2~net~gaw~ar~422731074191~kw~hiscox%20insurance~mt~e~cmp~Br...
Replies
7
Views
1K
  • Question
Hi I need help and advice on knowing minimum cross sectional area CSA TN earthing conductor size please
Replies
3
Views
1K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
378

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks