a few questions can anyone please help.
on the second page particulars of installation at the origin, it states number of smoke alarms do you fill this in if you have fitted the smoke alarms yourself or do you still fill it in i.e put down 2 even if their is 2 smoke alarms in the house.
under main switch or circuit-breaker if it is a sub main do you put the main switch in this case a 61009 rcd or the mcb 60898 type 2 feeding the board.
is the max zs permited for a 60898 type 2 the same as a type b.
insulation resistance testing line/line what is this live to live on a ring main only.