The test cert is for a transportable building

I have fill in a test not done it since college, i dont know what to put in the max disconnection time for Bs60898 MCBs protected by a 63A 30ma RCD main switch, no circuit exceeds 32A

is it 0.4s for a TN system
is it 0.2s for a TT system
or
300ms for rcd

cheers
 
Are you an Electrician? if yes then you should know the answer, if no then should you be carrying out Electrical testing?
 
yes since 2009 had to do inspection and testing modular and certed on back of tradecard as regs changed during serving my time,only asking a question what section in the regs book as i couldnt see anything in appendix 6 i was just gonna put in 0.4 as that is the maximum i can be depending on circuit(worst case scenario) but was just looking for some advice
 
yes since 2009 had to do inspection and testing modular and certed on back of tradecard as regs changed during serving my time,only asking a question what section in the regs book as i couldnt see anything in appendix 6 i was just gonna put in 0.4 as that is the maximum i can be depending on circuit(worst case scenario) but was just looking for some advice

It will be in your on site guide mate
 
cheers mate by i cant find a reg that relates when you dont know what type of system the incoming supply is, I know table 41.1 gives you max disconnection times
 
How come you can't find out what type of supply it is?

Because it is a portable cabin type affair, supply source unknown and variable.

If it were me I would probably T+I for the most onerous conditions and use the TT disconnection times.
 
Last edited:
cheers mate i was looking for some advice because i wasnt sure myself what to do but then i thought there was a reg or guidance somewhere for when i was getting to check my osg or regs and then getting told i wasnt a spark, just started the job reffitng cabins to spec for clients
 
You obviously cannot enter the supply characteristic bits on the form, but I would be T+I ing to make sure it is suitable for all types of supply likely to be connected, ie. and that the disconnection times meet TT, RCD present etc...etc..

I would have thought when it is connected up on site it would need checking again to make sure it is compliant.
 

Reply to help filling in niceic test certs please in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
556

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top