Hi Guys
For the last few weeks i have been sorting out some iffy stuff at a relatives home .Some of which was exceptionally iffy.
Heres a description of the latest one i have found .
two storey semi with attic
upstairs ring main single socket has a spur taken from it (no fused unit for isolation) which feeds a double socket in a cupboard .
This double in turn has two plugs in it .
Both the plugs are wired with 1mm twin n earth lighting cable.
plug 1 feeds an external pir lamp at the front door of the property .
plug 2 feeds a series of flo fittings in the attic via an antique neon switch which accesory is broken not securely fixed.
I would welcome any pointers as to the best remedy.
My thoughts are fit a fcu at the single socket then wire the exterior light correctly to this .
find the upstairs lighting circuit and break into that with a 5amp terminal unit and feed the lights from there.
However is there a way to use the single feed from the ring suitablly fused for isolation to feed both the attic lights and the exterior light.
Many thanks
72-van
For the last few weeks i have been sorting out some iffy stuff at a relatives home .Some of which was exceptionally iffy.
Heres a description of the latest one i have found .
two storey semi with attic
upstairs ring main single socket has a spur taken from it (no fused unit for isolation) which feeds a double socket in a cupboard .
This double in turn has two plugs in it .
Both the plugs are wired with 1mm twin n earth lighting cable.
plug 1 feeds an external pir lamp at the front door of the property .
plug 2 feeds a series of flo fittings in the attic via an antique neon switch which accesory is broken not securely fixed.
I would welcome any pointers as to the best remedy.
My thoughts are fit a fcu at the single socket then wire the exterior light correctly to this .
find the upstairs lighting circuit and break into that with a 5amp terminal unit and feed the lights from there.
However is there a way to use the single feed from the ring suitablly fused for isolation to feed both the attic lights and the exterior light.
Many thanks