Hi all,

I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone please help me understand how to get the answer as I just cant seem to work it out!

Thank you advance!

Voltage drop of a single-phase distribution circuit supplying a power distribution board in a remote building is to be verified as part of the periodic inspection and testing within a workshop complex. The installation forms part of a public 400/230 V TN-S system.
The circuit has a measured R1+Rn value of 0.15 Ω and an Ib of 60 A. The circuit protective device has an In of 80 A, see Figure 5.
What is the maximum acceptable voltage drop for this distribution circuit if the highest circuit voltage drop on DB-3B is 5.0 V?
[ElectriciansForums.net] Help me work out volt drop please....

a) 11.5 V
b) 6.9 V
c) 6.5 V
d) 1.5 V
 
Total Maximum permitted VD from Main DB to end of final circuit from DB3 = (say5%)
Therefore max permitted VD on distribution circuit = 5% - 5.0volts (from question) =
 
Im sorry this is probably the bit that is confusing me, could you explain please?
The maximum permissible VD at the farthest point of any circuit (except a lighting circuit) is 5% or 11.5 volts
The volt drop on one of the circuits from DB3 is already calculated to be 5volts (in question)
Therefore 11.5 - 5 = 6.5vots permitted to be 'dropped' on distribution circuit.

As #6, too much information given beforehand.
 
So it's asking for maximum permissable v.d and its single phase so 5% of 230v = y (This is the total v.d you are allowed). You are told that a circuit from DB3 has a v.d of 5v so y - 5v = max v.d allowed for the distribution circuit.
 
simple. you are allowed 5%, or. 11.5V in total . as the DB3 has a VD of 5V already, your distribution circuit max. VD id 11.5 - 5.0 =6.5V. answer (c),
 
People have already responded to your other thread.
 
Last edited:

Reply to Help me work out volt drop please.... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top