The guidance for 2kW dedicated circuit, is only informative in App 15, granted.
 
Very true with regards to the kettle but the Regulations for 2kw is not for portable appliances and the cause of this problem was pushing the 13A fuse to its limit for prolonged periods of time.
 
The guidance for 2kW dedicated circuit, is only informative in App 15, granted.
I realise the IET don't have all the answers but in this case I think they have it right on the nail.
 
From an electrical point of view it would be best to have a specific 16A radial circuit for the heater on a higher rated (16A+) plug and socket arrangement.
The rating of the immersion means that it is pulling the maximum current that a BS1363 socket should take so any slight anomalies may cause melting such as you have seen. The same thing happens with standard immersion heaters on plug and socket or fused spur arrangements.
With the circuit installation you have you are unable to avoid requiring a 13A fuse at some point, presumably the wifi socket may be fused, the plug in the wifi socket will be fused and in the current set up the plug on the outside is also fused.
Each fuse (and each connection) is a potential point of failure.
The wifi socket must also be close to its rated limit as they are often limited to 10A or even 5 A.
The simplest solution would be to have a 16A socket installed outside instead of the double socket and still plugged in as you have it now inside, however this will only transfer the possibility of failure to the wifi socket and the plug which is used inside and will not address the heavy loading on the ring, although if it is only used at night the loading on the ring will probably be low.
 
I believe somewhere there is a requirement for immersions not to be on plug tops but I doubt this instance is applicable.
 
From an electrical point of view it would be best to have a specific 16A radial circuit for the heater on a higher rated (16A+) plug and socket arrangement.
The rating of the immersion means that it is pulling the maximum current that a BS1363 socket should take so any slight anomalies may cause melting such as you have seen. The same thing happens with standard immersion heaters on plug and socket or fused spur arrangements.
With the circuit installation you have you are unable to avoid requiring a 13A fuse at some point, presumably the wifi socket may be fused, the plug in the wifi socket will be fused and in the current set up the plug on the outside is also fused.
Each fuse (and each connection) is a potential point of failure.
The wifi socket must also be close to its rated limit as they are often limited to 10A or even 5 A.
The simplest solution would be to have a 16A socket installed outside instead of the double socket and still plugged in as you have it now inside, however this will only transfer the possibility of failure to the wifi socket and the plug which is used inside and will not address the heavy loading on the ring, although if it is only used at night the loading on the ring will probably be low.
A bit long winded but Yes
 
I believe somewhere there is a requirement for immersions not to be on plug tops but I doubt this instance is applicable.
GN1 advises a plug and socket set up for connecting immersion heaters is not recommended id imagine due to the 13amp plug and fuse being subject to their maximum loading for lengthy periods of time daily.

I've also come across 13amp fused Spurs feeding immersion heaters on economy 7 installations during eicr s , where the spur shows signs if thermal damage and in some cases the spur has cracked across the plate but the fuse is still intact, all be it melted into the plastic holder.
 
Last edited:
What does it show, when plugged into the socket without the Wi-Fi thing?

i.e. socket turned off?

With the socket turned off (I.e the wifi adaptor off) it shows no N. With it turned on it's all normal. I presumed it's how it works to keep the wifi signal active?
 
@OP. if this appliance is in your van, does that mean that you plug it in at customers' premises. i.e. on site, as opposed to at home? if so, you would risk overloading their circuit/s. only solution would be to replace the heater with a lower power unit.
 
@OP. if this appliance is in your van, does that mean that you plug it in at customers' premises. i.e. on site, as opposed to at home? if so, you would risk overloading their circuit/s. only solution would be to replace the heater with a lower power unit.


That's a good point. Usually I plug it in at home and turn it on for an hour before I leave. It general stays hot enough all day - so I don't need to plug it in.

But on occasion I do plug it in at customer's houses via my extension lead and have never had a problem. Although as the tank is already warm, I doubt it 'fires' for long before reaching the required temp.

The other guy who I work with has been doing this job for 13 years, and has used this set-up for all that time with no issues - except for the element blowing every three months or so (although that's probably more to do with the sodium hydroxide in the tank!)

So - would the best solution (given that there's is some debate about best practice) to run a dedicated feed from the CU out of the house and to a 16A rated socket with 16A plug?

As I need to plug it into the van would a 16A socket and plug (on the element) in the van also be required? I'm presuming so.
 
That's a good point. Usually I plug it in at home and turn it on for an hour before I leave. It general stays hot enough all day - so I don't need to plug it in.

But on occasion I do plug it in at customer's houses via my extension lead and have never had a problem. Although as the tank is already warm, I doubt it 'fires' for long before reaching the required temp.

The other guy who I work with has been doing this job for 13 years, and has used this set-up for all that time with no issues - except for the element blowing every three months or so (although that's probably more to do with the sodium hydroxide in the tank!)

So - would the best solution (given that there's is some debate about best practice) to run a dedicated feed from the CU out of the house and to a 16A rated socket with 16A plug?

As I need to plug it into the van would a 16A socket and plug (on the element) in the van also be required? I'm presuming so.
I imagine you would need a circuit from your CU to a 16 Amp socket, your heater would require a 16 Amp plug top to enable you to plug it into the 16Amp socket wired from your CU how you would manage at the customer premises is a different problem.
 

Reply to Help - melted plug - why? in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

The same socket can be used for different appliances, such as kettles... which will draw more than 5A The size of the cable determines how much...
Replies
4
Views
844
Most appliances come with a plug fitted if they are rated 13amp.or under. If not I would just fit a plug top. If it's rated greater than 3kw then...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top