Hi guys, wonder if you could help,
I have been asked to supply power and lighting to a cabin/summerhouse 35 metres from house C.U.
Customer has already installed 7 core 2.5mm SWA underground (he says he "acquired it" from a friend at YEDL)
All calculations are fine for a load max of 2Kw (volt drop approx 5.9v)
My problem is, because it is 7core, the guy wants to include within it, a seperate lighting cct for tree illumination, controlled at the house end when the cabin is isolated.
Just like to know your thoughts regarding safe isolation at house end for anyone in the future working on either circuit, i.e. how you would supply both circuits.
1) from 2 seperate spare ways in c.u. suitably protected
2) create a distribution circuit, either 25mm tails & henley block or 6mm from c.u, to a 2 way "garage" cu and then feed from there within the swa (adaptor box if nescessary)
Also, sorry to be a pain, your thoughts on protection at cabin end.
System is TN-S
No extraneous conductive parts at cabin end
Sorry for long post
Thanx
Mick
 
Reg 521.7 Two or more circuits are allowed in the same cable provided requirements of section 528 is met. So that would mean other srvices and you are ok with that as far as I can see.

As your only working with a 2.5mm and that is quite a run for that size cable, if there were spare ways in the exising CU I would use them. Depending on what type of board it was I would go for RCBO's on a non protected side.

If you have just a split board with no non protected side then perhaps a new 2 way board would be better as you don't want the chance of nuicience tripping. Then RCBO.

I would terminate into an adapatable box first and use a little piece of din rail with klippons. Terminate all 7 cores that way.

TN-S then Earth OK. No bonding issues with no services in the Cabin. Again terminate into an adaptable box. As the socket will give you full isolation and function switching that will be ok. You may though think about fitting a double pole switch for the light if you having a switch in the Cabin.
 
Check the voltage drop for the lighting circuit.

Steve.
Hi Steve, thanx for post,
was more concerned about safe isolation at house end, forgot to mention load on lighting.
No more than 1Kw tops absolute max!! Couple/ three 100watt halogens, couple of elv circuits, and room for expansion, so 1000/230= 4.35amps max
18mv/am x 4.35a x 35metres = 2.7% just within 3% limit.
What are yor thoughts on light switching control at house end?
Cheers
Mick
 
Hi Steve, thanx for post,
was more concerned about safe isolation at house end, forgot to mention load on lighting.
No more than 1Kw tops absolute max!! Couple/ three 100watt halogens, couple of elv circuits, and room for expansion, so 1000/230= 4.35amps max
18mv/am x 4.35a x 35metres = 2.7% just within 3% limit.
What are yor thoughts on light switching control at house end?
Cheers
Mick
Cant see a problem as long as the switch can take the load.

Steve.
 

Reply to Help, multiple circuits external supply 7 core SWA in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top