installed a new cu for some one yesterday, its a tt system incoming voltage 240v and incoming earth from spike 100ohms, all the circuits tested fine every thing works as it should!
now today i went to the same place to change the other small db that supply's 3 circuits the other end of the building. 1x ring and 2x lighting circuits, this small board is fed from the main db with a 40a type b mcb covered by the 63a 30ma rcd. and a 16mm2 3 core swa.
so i did the board, all circuits tested and are good,and with in coming ze of 78.6ohms.
where iv started to have problems is with the rcd test.
i cant get it to trip at x1 or x5 and it doesnt even trip the rcd on the main db side.
iv tried 3x new rcds thinking that it was a faulty rcd but still nothing and its not my tester as iv tried my other tester and have tested on a known working circuit on the main db.
iv had to leave the power turned off tonight as i wasnt happy about leaving it on knowing that it didnt trip when put under fault conditions.
any on got any ideas?
now today i went to the same place to change the other small db that supply's 3 circuits the other end of the building. 1x ring and 2x lighting circuits, this small board is fed from the main db with a 40a type b mcb covered by the 63a 30ma rcd. and a 16mm2 3 core swa.
so i did the board, all circuits tested and are good,and with in coming ze of 78.6ohms.
where iv started to have problems is with the rcd test.
i cant get it to trip at x1 or x5 and it doesnt even trip the rcd on the main db side.
iv tried 3x new rcds thinking that it was a faulty rcd but still nothing and its not my tester as iv tried my other tester and have tested on a known working circuit on the main db.
iv had to leave the power turned off tonight as i wasnt happy about leaving it on knowing that it didnt trip when put under fault conditions.
any on got any ideas?