coxy84

installed a new cu for some one yesterday, its a tt system incoming voltage 240v and incoming earth from spike 100ohms, all the circuits tested fine every thing works as it should!

now today i went to the same place to change the other small db that supply's 3 circuits the other end of the building. 1x ring and 2x lighting circuits, this small board is fed from the main db with a 40a type b mcb covered by the 63a 30ma rcd. and a 16mm2 3 core swa.

so i did the board, all circuits tested and are good,and with in coming ze of 78.6ohms.
where iv started to have problems is with the rcd test.

i cant get it to trip at x1 or x5 and it doesnt even trip the rcd on the main db side.

iv tried 3x new rcds thinking that it was a faulty rcd but still nothing and its not my tester as iv tried my other tester and have tested on a known working circuit on the main db.

iv had to leave the power turned off tonight as i wasnt happy about leaving it on knowing that it didnt trip when put under fault conditions.


any on got any ideas?
 
are their two rcd's in series, ie for discrimination?
is ur tester on ac or dc setting or something, i.e the correct setting............just trying to narrow down problem?

my tester is on the right setting i belive,

100a main switch-30ma rcd -40a mcb-16mm2 swa-100a main switch-63a 30ma rcd-32a mcb for ring
(main duel rcd db) (cable to 2nd db) (2nd db)
 
mate from your post it appears you have 2 RCD's in series. Test the plug top fuse or test with the individual leads in the back of the socket and see if that works.
Not sure if this may affect it, if but have you mixed up the neutrals into the RCD when changing it?? As in the supply neutral into the load side of the RCD? Easily done.
 
Last edited:
Sorry just seen the post above!! forget the second part! Wasnt sure if that would affect it anyway! Try doing an RCD test in your house and if it doesnt work then maybe the tester is faulty if you have it on the right settings.
 
my tester is on the right setting i belive,

100a main switch-30ma rcd -40a mcb-16mm2 swa-100a main switch-63a 30ma rcd-32a mcb for ring
(main duel rcd db) (cable to 2nd db) (2nd db)

If you are sure that the system is earthed,and your tester is functioning,and you have eliminated a faulty RCD..(almost impossible given that there are 2 in series and you have changed 3 times)...they WILL trip.
My guess would be that you have not correctly wired the RCD's into the DB's...........the fact that neither are tripping when a test on DB2 should trip both would back that up.

Edit....try testing directly the output side of the RCD in the DB with probes ,which will confirm a functioning RCD
 
Last edited by a moderator:

Reply to help needed! my brains been frazzled! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
989
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
673
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top