C

coxy84

installed a new cu for some one yesterday, its a tt system incoming voltage 240v and incoming earth from spike 100ohms, all the circuits tested fine every thing works as it should!

now today i went to the same place to change the other small db that supply's 3 circuits the other end of the building. 1x ring and 2x lighting circuits, this small board is fed from the main db with a 40a type b mcb covered by the 63a 30ma rcd. and a 16mm2 3 core swa.

so i did the board, all circuits tested and are good,and with in coming ze of 78.6ohms.
where iv started to have problems is with the rcd test.

i cant get it to trip at x1 or x5 and it doesnt even trip the rcd on the main db side.

iv tried 3x new rcds thinking that it was a faulty rcd but still nothing and its not my tester as iv tried my other tester and have tested on a known working circuit on the main db.

iv had to leave the power turned off tonight as i wasnt happy about leaving it on knowing that it didnt trip when put under fault conditions.


any on got any ideas?
 
If you are sure that the system is earthed,and your tester is functioning,and you have eliminated a faulty RCD..(almost impossible given that there are 2 in series and you have changed 3 times)...they WILL trip.
My guess would be that you have not correctly wired the RCD's into the DB's...........the fact that neither are tripping when a test on DB2 should trip both would back that up.

Edit....try testing directly the output side of the RCD in the DB with probes ,which will confirm a functioning RCD


i will do in the morning! cheers
 
stick your tester on 500mA and try it @ 5xI delta N

If it won't trip then maybe it's back to triple check the wiring.

Cant see it...the meter has been confirmed ok...the RCD's have pretty much been confirmed ok by virtue of being changed several times....if they are correctly installed they must trip @1x never mind 500ma....I still think they are not installed in the DB correctly.
Do make sure we get the outcome Coxy84....an intriging problem.
 
Last edited by a moderator:
Cant see it...the meter has been confirmed ok...the RCD's have pretty much been confirmed ok by virtue of being changed several times....if they are correctly installed they must trip @1x never mind 500ma....I still think they are not installed in the DB correctly.
Do make sure we get the outcome Coxy84....an intriging problem.



i will go over every thing in the morn! ill be sure to let you know what the out come is!
 
where is the second db fed from an mcb in the first board if so try and dissconnect the second db from the installation then try the first rcd or maybe if the earth path isnt good enough maybe its not putting enough mA down through the rcd if you get me also you could try and put you tester on 100mA at 5x and see if it trips then
 

Reply to help needed! my brains been frazzled! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
456
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
683
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
745

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top