A

Aquaman

Hello all.

I am upgrading my bungalow fuse box to a new split load CU. My circuits on the fuse box were, 1. Cooker, 2. Heat pump and sockets, 3. Immersion heater, 4. Lights.

My new CU is a split load CU, to which I decided to separate the circuits between 2 RDC's in the following way, (From right to left) Main Switch, then RCD 1 with Cooker on a 32A MCB, then Immersion on a 16A MCB, then the lights on a 6A MCB followed by 2 spare spaces.

Then I put RCD 2 with the sockets on a 32A MCB, followed by the shower pump on a 16A MCB.

I did all of the tests such as, continuity, method 1 and 2, IR.

It's a bungalow, and it appears that the sockets are not a ring, but a radial so can't do end to end tests etc.

The problem is that the first RCD trips out as soon as I energise the lighting MCB and the 2nd RCD trips out as soon as I energise the sockets circuit.

Any help would be gratefully appreciated.
 
Last edited by a moderator:
If the sockets are a radial and you have them on 32a have you got them wired in 4mm?

The RCD's trip when theres a leakage to earth, i suggest you go through the test procedure again + check that you haven't got the neutrals mixed up.

- - - Updated - - -

I am officially so slow at typing today, thats the second thread in a minute that Dillb has beaten me lol.
 
The sockets were on one MCB/fuse rated at 32/30 amps, now they're on two.....
I'm not keen on "it appears that the sockets are not on a ring" if you did your testing properly you'd have found that out for definite
 
I have 3 neutral bars.

I initially thought the sockets would be in a ring, but the end to end tests failed so assume it's a radial as nothing proves a ring circuit.

I thought it may be a borrowed neutral and will check each neutral bar tomorrow.

Anywhere else I should check for a BN?

Thanks
 
Why have you decided to load the one rcd with both radial circuits,which presumably are supplying all your sockets and on 32 amp mcb (4mm assumed) ? What is the reasons for this decision
 
It was definitely a ring some time ago, I presume the T+E is 2.5 and 1.5 in your case if protected by 30A fuse, where now then you have 2 radials each on 32A mcb’s, NOT GOOD. Makes me question, are you really should be doing this…
 

Reply to Help needed on CU Upgrade in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
319
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top